Acceptable resistance when adding resistance to supervisory inputs
  • Acceptable resistance when adding resistance to supervisory inputs
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 01:07 PM
What is the acceptable range of tolerance for resistance on a supervisory input.
  • i1 controllers
  • i2 controllers
  • b3 controllers
  • I/O modules
Doors are being retrofitted, and the resistors that are installed are not 10K ohm and are inaccessible.
The tolerance for the resistance on supervisory inputs is +/- 3%.