A Vista OPC server cannot access objects on another Vista server other than the one it is installed on
  • A Vista OPC server cannot access objects on another Vista server other than the one it is installed on
  • Jonas_Brissman
    Jonas_Brissman
‎2018-09-06 01:03 PM
If having a Vista network and a OPC server installed on one Vista server can a OPC client connecting to the OPC server read values from another Vista server in the network?
Vista 5.1.6
OPC server 1.6.2
No it is only possible for the OPC client to read values on the Vista server where the Vista OPC server is installed.
This is to avoid a lot of communication between the Vista server nodes which is pretty slow.
Install a OPC server on every Vista server.
  • 6622