7798C stops communicating after BIN file download

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • 7798C stops communicating after BIN file download
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2246 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

7798C stops communicating after BIN file download

Picard Product_Support
‎2018-09-06 12:09 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:39 AM

Issue

  • 7798C stops communicating after BIN file download
  • Is the 7798C supported in the older versions of I/NET Seven (1.14 and below).
  • How to reset the 7798C hardware (i.e. place into boot mode) if no communication is possible with the 7798C   

Product Line

TAC I/NET

Environment

  • I/NET Seven 1.14 and lower
  • I/SITE LAN 7798C

Warning

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Cause

I/NET revision 1.14 and lower does not support 7798C and can mistakenly be assumed by the I/NET Host software as a 7798B.  If a software restore is completed to the 7798C with these revisions, it disables the device from communicating via the Controller LAN and disables any communication via the serial port with the Hand Held Console (HHC) software.  

Resolution

If you have downloaded the incorrect BIN file (i.e. 7798) to the 7798C, the handheld console software will not work, and hence, the device can not be placed back into a boot state, allowing the correct BIN file to be restored to the 7798C. 

If the serial port is still configured/enabled for direct connection via the onboard TAP, this is the easiest solution to try a software restore to blank out 7798C with the correct BIN file.

If either of these options are not available, the following steps can be performed very carefully directly on the hardware:

  1. Very Important:  Make sure you turn OFF the power to the 7798C unit. If you fail to remove power, this process could damage the board.  If unsure, please contact Product Support
  2. On the top edge of the board is the EPROM, and just below are two RAM chips.
  3. Between the EPROM and the two RAM chips are two mustard-colored capacitors (Labeled C2 & C3)
  4. If you short across each Capacitor, one at a time, this will take the device to boot.
  5. If you still have issues with the device, sending the 7798C in for repair is recommended.

Once the device is communicating again, the correct firmware can be restored to the 7798C. At this point, you should be using I/NET Seven revision 1.17 or above.

Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 8312
  • RobertAndriolo24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore