Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

4 Channel xP Modules still reserves 8 Channels in Security Expert

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • 4 Channel xP Modules still reserves 8 Channels in Security Expert
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • David_Kendrick
    David_Kendrick

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1119 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

4 Channel xP Modules still reserves 8 Channels in Security Expert

Admiral David_Kendrick Admiral
‎2021-04-28 07:07 AM

Last Updated: Picard RobertAndriolo Picard ‎2021-04-29 03:44 AM

Issue

A 4 Channel xP Module such as an xpBD4 appears to reserve 8 channels in Security Expert

Product Line

EcoStruxure Security Expert

Environment

xP Expansion Modules

Cause

xP Expansion Modules were originally created for the Continuum Access control system but through transitions are now being used with Security Expert as well. When used in Continuum, a 4 digital channel xP Module would reserve 4 channels only. However under Security Expert that same 4 digital channel xP Module will reserve 8 channels instead.

 

Continuum ACX5740 plus xPBD4 plus xPD18

ACX5740 Inputs 01 -12 First 12 channels
xPBD4 Inputs 13 -16  Next 4 channels
xPDI8 Inputs 16 - 24 Next 8 channels

Security Expert SP-ACX plus xPBD4 plus xPD18  (Note all SP-ACXs have ACX 5740 I/O counts)

SP-ACX Inputs 01 - 12 First 12 channels
xPBD4  Inputs 13 - 20 Next 8 channels
xPDI8  Inputs 21 - 28 Next 8 channels

Resolution

Some of the channel reservation under Security Expert has changed relative to how it used to be handled in Continuum, so now even for a 4 digital channel xP module such as an xPBD4, 8 Channels are automatically reserved by design even if only 4 of those channels are actually used.

To check all Input, Output, Digital and Analogue xP Channel reservation scenarios under Security Expert please refer to AN 310 Security Expert - xP Module Configuration - Application Note  (for this digital input example, page 7 shows the relevant channel assignment).

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • DavidKendrick21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore