1401 when reloading a controller.
  • 1401 when reloading a controller.
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 12:51 PM
During reload Continuum throws a 1401 error - item cannot be found.
All Controllers
There is an problem with an object link (such as an alarm link to an alarm enrollment object) that is attached to an object within the controller.
  1. Reload the contents of the controller by class to determine which object class is causing the error.
  2. Once the object class has been determined reload each object in that class separately until the problem objects are found.
  3. Either delete and rebuild the objects, or clear each object link and reestablish that link.
  4. Reload to verify that error is no longer occurring.
  • 7010