Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

Software for monitoring multiple APC UPS systems

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Software for monitoring multiple APC UPS systems
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
135
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
sesa116209_brid
Ensign sesa116209_brid Ensign
Ensign

Posted: ‎2019-10-25 12:16 PM . Last Modified: ‎2020-12-02 04:30 AM

1 Like
6
8363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 12:16 PM . Last Modified: ‎2020-12-02 04:30 AM

Software for monitoring multiple APC UPS systems

I would like to find out if there is an app that our customer can use to monitor the status of multiple APC UPSs over the network at the same time.  All UPSs are by APC and are equipped with the network management cards.  Customer can access the UPS status via NMC but only one at a time.  APC PowerChute Network Shutdown (PCNS) is currently installed on all the servers and workstations.  APC told me there is no app that APC has that would allow us monitor all UPSs from one interface.  This can't be the first time a customer asks for such an application.  This customer has multiple sites with about 5 APC UPSs per standalone site.

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa116209_brid
Ensign sesa116209_brid Ensign
Ensign

Posted: ‎2020-10-14 06:04 AM

2 Likes
0
7682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-14 06:04 AM

Here is a link for a related forum discussion in APC forums for anyone interested.

 

https://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/11388/mana...

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Omaelk
Janeway Omaelk
Janeway

Posted: ‎2019-10-29 06:40 AM

0 Likes
2
8336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-29 06:40 AM

Hello @sesa116209_brid , thanks for your question

 

@Benji , @Matt_Curry  any inputs on that? 

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-10-13 05:12 AM

In response to Omaelk
0 Likes
1
7709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-13 05:12 AM

@Omaelk @sesa116209_brid or others

 

Any word on how to monitor the status of multiple APC UPSs? 

 

We face the same challenge, having around 50 different locations throughout the country with each one server and one APC UPS. At the moment the servers are running APC PowerChute Business Edition v7.00. Ofcourse we need to upgrade the version but we also want manage/monitor the UPSs from one interface. 

 

Looking forward to an answer/advice.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sesa116209_brid
Ensign sesa116209_brid Ensign
Ensign

Posted: ‎2020-10-13 05:38 AM

In response to Anonymous user
0 Likes
0
7707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-13 05:38 AM

@Anonymous user , fyi I did not receive any solutions as a result of this post, the customer is still logging into 1 UPS at a time.  Thanks.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2020-10-13 04:54 PM . Last Modified: ‎2023-02-06 10:38 PM

1 Like
1
7694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-13 04:54 PM . Last Modified: ‎2023-02-06 10:38 PM

Today at least, there is no APC community here. You may want to visit https://community.exchange.se.com/t5/APC-UPS-Critical-Power-Cooling/ct-p/critical-power-cooling-rack... and post your question there.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sesa116209_brid
Ensign sesa116209_brid Ensign
Ensign

Posted: ‎2020-10-14 05:50 AM

In response to CraigEl
0 Likes
0
7689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-14 05:50 AM

Thank you, I wish someone told me that a little shy of a year ago.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sesa116209_brid
Ensign sesa116209_brid Ensign
Ensign

Posted: ‎2020-10-14 06:04 AM

2 Likes
0
7683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-14 06:04 AM

Here is a link for a related forum discussion in APC forums for anyone interested.

 

https://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/11388/mana...

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore