Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Ask questions, get advice from experts and peers on Digital Automation & Energy Management.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-27 04:39 AM
Hi everyone!
I want to read the DI6 from my ATV320 with my PLC TM262. It is the first time I am using the FB MC_ReadDigitalInput and when I send the program to the PLC I get from the function block itself an error "104 The address of the remote device is incorrect".
I attach some screenshots from my project (simulation mode, so it does not show the error live).
I thank any suggestions offered.
If maybe I need to use another type of FB I can do that too, but I have searched everywhere and I do not find clear information about how to do it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-02 01:42 PM
Hello everyone,
I found a way to do it, so I wanted to share in case someone else had the same question.
Some basic steps to read an input with the drive ATV320:
1) You must assign a logic input to the function you need (https://www.se.com/us/en/faqs/FA310914/)
2) You can use the register 5202 to read the inputs of your drive (https://www.se.com/eg/en/faqs/FA320881/). Here they explain it with the ATV61 and ATV71 (https://www.se.com/us/en/faqs/FA175310/) Here you can see that it is still the same logical address for the ATV320(https://www.se.com/in/en/download/document/NVE41316/)
3) I am attaching images to this post about where to put the logical address, in case its useful for someone.
4) After creating the variable in the I/O Mapping of your drive, you can read it with a FB of your own or you can call it directly using the memory address, it's up to you.
I hope it helps!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-02 01:42 PM
Hello everyone,
I found a way to do it, so I wanted to share in case someone else had the same question.
Some basic steps to read an input with the drive ATV320:
1) You must assign a logic input to the function you need (https://www.se.com/us/en/faqs/FA310914/)
2) You can use the register 5202 to read the inputs of your drive (https://www.se.com/eg/en/faqs/FA320881/). Here they explain it with the ATV61 and ATV71 (https://www.se.com/us/en/faqs/FA175310/) Here you can see that it is still the same logical address for the ATV320(https://www.se.com/in/en/download/document/NVE41316/)
3) I am attaching images to this post about where to put the logical address, in case its useful for someone.
4) After creating the variable in the I/O Mapping of your drive, you can read it with a FB of your own or you can call it directly using the memory address, it's up to you.
I hope it helps!
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.