Posted: 2022-03-02 11:52 AM
Isn't there a parameter for configuring the duct inlet size for VAV box controllers (V2's), so that it can calculate the air flow correctly? Where is that found, in the balancer tool?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-03-02 02:43 PM
You don't input the inlet size, you input the Rated Box flow at 1" WC. See attached page from the Commissiong Tool and Flow Balance Tool User guide. This value is often found on a sticker on the side of the box or in the flow data in the box specifications. If you can't find this information you may need to contact the box manufacturer.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-03-02 02:43 PM
You don't input the inlet size, you input the Rated Box flow at 1" WC. See attached page from the Commissiong Tool and Flow Balance Tool User guide. This value is often found on a sticker on the side of the box or in the flow data in the box specifications. If you can't find this information you may need to contact the box manufacturer.