MNB-1000 set up

Ask the Community

Ask questions, get advice from experts and peers on Digital Automation & Energy Management.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Support
  • Ask the Community
  • MNB-1000 set up
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
35
chris_clerc
Administrator chris_clerc Administrator
8
MikaelKrantz
Guinan MikaelKrantz Guinan
7
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Ask the Community
Start a Topic
Krobbins
Krobbins
Cadet

Posted: ‎2023-03-30 05:23 AM

0 Likes
2
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-30 05:23 AM

MNB-1000 set up

We have a new to us MNB-1000.  We had not luck seeing it with WPT commissioning tool, so set it back to factory defaults.  No change.  WPT is not giving any errors or popups.  We have tried both RJ45 ports, I think the lower one is ethernet, but have not been able to confirm this.

Solved: MNB-1000 Set IP after factory reset - Communities  is very close to our issue, but we are not getting any pop up error messages.

When we use WPT on network with our running MNB-1000s and Jaces, they all show up in the commissioning tool.

If we plug into the MNB-1000 with a PC running wireshark on it, should we see anything?  We didn't, could this be due to ICMP being disabled?  This is not meant as a red herring, just without the ability to ping, how can we determine if the MNB-1000 can communicate at all?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2023-03-30 05:26 PM . Last Modified: ‎2023-03-30 10:19 PM

0 Likes
1
3564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-30 05:26 PM . Last Modified: ‎2023-03-30 10:19 PM

After a reset or fresh from the factory the MNB-1000 IP and MS/TP ports are disabled. The Ethernet port is the only port enabled. You need to set WPCT to BACnet Ethernet to access the MNB-1000 controller via its Ethernet port. Once you have gained access, its BACnet/IP port can then be enabled. 

 

Set up Ethernet communications in WorkPlace Commissioning Tool as follows:

  1. Open the File menu and select Connect to open the Communications Settings dialog box
  2. Verify that the BACnet radio button is selected.
  3. If you need to change timeout settings, click Advanced. The Advanced Settings dialog box opens
  4. In the Communications Settings dialog box, click Change.
  5. In the BACnet Communications Settings-Protocol dialog box click the Ethernet radio button, and then click Next to continue.
  6. Review the information and settings in the BACnet Communications Settings-Ethernet Protocol dialog box  select a different interface if necessary, and then click Finish.

    TinyTake31-03-2023-11-23-24.png

  7. The Communications Settings dialog box appears. Verify the settings shown, and then click Change to revise the settings or OK to accept. TinyTake31-03-2023-11-25-23.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Krobbins
Krobbins
Cadet

Posted: ‎2023-03-31 05:21 AM

In response to CraigEl
0 Likes
0
3552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-31 05:21 AM

After following those steps, a few times, I select communications pull down, then 'browse', show all devices, browse settings....network or global?  Nothing shows up in the window, either way, '0 devices found'.

Should the dip switches all be off?  

Laptop is set to 10.1.10.212 with ethernet cable plugged into upper RJ45 port on MNB.

I don't know if I am doing something wrong or we have a bad device.

Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore