Been looking everywhere trying to find something to cross this to or find a replacement. Anyone know?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-04 05:47 PM
The MA407-701 actuator was a dual 120/240Vac motor 16inlb torque with end switch and 113 degree rotation. We do not offer an actuator like this any longer. The closest would be two different "functional" replacements:
MA-418-500 This is a 120Vac 60inlb torque with end switch and 180 degree rotation.
MA-419-500 This is a 240Vac 60inlb torque with end switch and 180 degree rotation.
You will need to select the correct voltage model for your requirements and will have to adjust the rotation by the damper linkage. You may get close to 113 degree rotation but won't get exact.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-04 05:47 PM
The MA407-701 actuator was a dual 120/240Vac motor 16inlb torque with end switch and 113 degree rotation. We do not offer an actuator like this any longer. The closest would be two different "functional" replacements:
MA-418-500 This is a 120Vac 60inlb torque with end switch and 180 degree rotation.
MA-419-500 This is a 240Vac 60inlb torque with end switch and 180 degree rotation.
You will need to select the correct voltage model for your requirements and will have to adjust the rotation by the damper linkage. You may get close to 113 degree rotation but won't get exact.