Posted: 2023-12-06 05:22 AM
Hi,
First post in here so thank you in advance and go easy on me. Trying to create and extended log on the ES that binds to a Trend Log on an AS-P on a different IP range in a separate building. The binding shows an unresolved path and trying to understand is this is a configuration issue in EBO or whether it's a firewall issue that i need our IT colleagues to look at.
There are comms between the ES and AS-P but for some reason this path remains unresolved.
Anyone had any experience of this and what was the resolution? Any tips on how i can rule out one or the other?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-07 02:51 PM
@BenYeates it's nearly always a firewall issue, EBO requires it's communications ports open in both directions since the AS-P needs to contact the ES with new data, not just upon a request from the ES.
The following Knowledge Base article should assist with troubleshooting the issue:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-07 02:51 PM
@BenYeates it's nearly always a firewall issue, EBO requires it's communications ports open in both directions since the AS-P needs to contact the ES with new data, not just upon a request from the ES.
The following Knowledge Base article should assist with troubleshooting the issue: