Building Operation Software Administrator - Stopping

Ask the Community

Ask questions, get advice from experts and peers on Digital Automation & Energy Management.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Support
  • Ask the Community
  • Building Operation Software Administrator - Stopping
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
35
chris_clerc
Administrator chris_clerc Administrator
8
MikaelKrantz
Guinan MikaelKrantz Guinan
7
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Ask the Community
Start a Topic
Solved
Jikku
Ensign Jikku
Ensign

Posted: ‎2023-01-24 08:58 AM

0 Likes
10
5266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 08:58 AM

Building Operation Software Administrator - Stopping

Hi Team,

 

My enterprise server status is showing as stopping however its not stopping for a while and hence I`m not able to login. Attaching the photo for your reference. 

 

Please help to resolve this issue. 

 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2023-01-24 10:30 PM

0 Likes
0
5205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 10:30 PM

If you don't need the EC then I'd suggest it be uninstalled. To reset the password you will need to contact support, see https://community.se.com/t5/Building-Automation-Knowledge/Forgotten-or-unknown-password/ta-p/4368

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2023-01-24 02:26 PM

0 Likes
3
5246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 02:26 PM

Please post the trace.log. The server logs are stored in the database folder. The full path depends on the software installed, and if the default path is used:
%ProgramData%\Schneider Electric [EcoStruxure|StruxureWare]\Building Operation [n.n]\Enterprise [Server|Central]\db\logs

Reply

Link copied. Please paste this link to share this article on your social media post.

Jikku
Ensign Jikku
Ensign

Posted: ‎2023-01-24 08:37 PM

In response to CraigEl
0 Likes
2
5234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 08:37 PM

Hi Craig,

 

Attached is the trace log for your reference. Please advise, 

Attachments
trace.log
Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2023-01-24 08:56 PM

In response to Jikku
0 Likes
1
5231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 08:56 PM

I've just noticed in your photo that you have an Enterprise Central install but you mention Enterprise Server. Seems like you have installed an EC by mistake.

Reply

Link copied. Please paste this link to share this article on your social media post.

Jikku
Ensign Jikku
Ensign

Posted: ‎2023-01-24 09:03 PM

In response to CraigEl
0 Likes
0
5228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 09:03 PM

For this project I`m only using Enterprise server, since I was not able to login repeatedly, I tried to stop and start the ES and ever since its stuck. i was able to login for the last 24 days and suddenly this issue occurred yesterday.   

Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2023-01-24 09:09 PM

0 Likes
1
5224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 09:09 PM

 I refer you back to your screenshot where I've highlighted the EC install.

TinyTake25-01-2023-04-05-13.png

I suggest that you uninstall the EC and see where you land.

Reply

Link copied. Please paste this link to share this article on your social media post.

Jikku
Ensign Jikku
Ensign

Posted: ‎2023-01-24 09:25 PM

In response to CraigEl
0 Likes
0
5216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 09:25 PM

Hello Craig,

 

I`m not able to uninstall the EC from system. No other folders are open yet it shows the same. Are there any other applications or services are to be stopped from windows?

 

 

 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2023-01-24 09:40 PM

1 Like
1
5212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 09:40 PM

Make sure that you have a backup of the ES database and stop both the EC and ES. Note that you will need to go to the Enterprise Server tab of the Software Administrator to stop it.

 

https://ecostruxure-building-help.se.com/bms/Topics/show.castle?id=10651

Reply

Link copied. Please paste this link to share this article on your social media post.

Jikku
Ensign Jikku
Ensign

Posted: ‎2023-01-24 10:01 PM

In response to CraigEl
0 Likes
0
5209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 10:01 PM

I was able to reinstall the ES and EC and now both systems are running. However not able to login to ES through localhost. Is there any way to reset the password for ES. 

Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2023-01-24 10:30 PM

0 Likes
0
5206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 10:30 PM

If you don't need the EC then I'd suggest it be uninstalled. To reset the password you will need to contact support, see https://community.se.com/t5/Building-Automation-Knowledge/Forgotten-or-unknown-password/ta-p/4368

Reply

Link copied. Please paste this link to share this article on your social media post.

Glenn13_12
Glenn13_12
Cadet

Posted: ‎2025-03-12 08:16 PM

0 Likes
0
2999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-12 08:16 PM

hello i want to connect to the server but the server say not installed 

Glenn13_12_0-1741835695926.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore