ACX 5740 Communication Failure

Ask the Community

Ask questions, get advice from experts and peers on Digital Automation & Energy Management.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Support
  • Ask the Community
  • ACX 5740 Communication Failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
35
chris_clerc
Administrator chris_clerc Administrator
8
MikaelKrantz
Guinan MikaelKrantz Guinan
7
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Ask the Community
Start a Topic
Solved
cpmacdon
Crewman cpmacdon
Crewman

Posted: ‎2022-03-08 08:45 AM

0 Likes
2
2639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-08 08:45 AM

ACX 5740 Communication Failure

Hello,

 

I am an end user/owner of a Schneider Electric access control system.  We have recently (within the last month) had three ACX5740 door controllers fail, all in the same manner.  Basically the unit appears off line in the system, door access is not functional, unable to communicate.  All LED's appear normal, units still respond to a PING, but I was unable to get them to return to Online status.  I first attempted the RAM clear, no luck.  I then performed an IP reset, unit will still respond successfully to a PING, but I am unable to connect to the configuration page through a web browser even when plugged directly into my laptop.  Any suggestions you can offer regarding how to fix this issue, and what may cause this to happen, would be greatly appreciated.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
cpmacdon
Crewman cpmacdon
Crewman

Posted: ‎2022-05-09 09:37 AM

In response to CraigEl
1 Like
0
2223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-09 09:37 AM

Thanks Craig!

 

As it turns out, the controller failures were caused by a network security scan that our IT team had switched to.

 

Long story short, Greenbone network security scan utility causes irreversible damage to ACX 5740 controllers.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2022-03-08 01:55 PM

1 Like
1
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-08 01:55 PM

You should probably contact your local SE office or EcoXpert and book a service visit. One failure can be seen as bad luck, but three makes me think it's something related to the environment or installation.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

cpmacdon
Crewman cpmacdon
Crewman

Posted: ‎2022-05-09 09:37 AM

In response to CraigEl
1 Like
0
2224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-09 09:37 AM

Thanks Craig!

 

As it turns out, the controller failures were caused by a network security scan that our IT team had switched to.

 

Long story short, Greenbone network security scan utility causes irreversible damage to ACX 5740 controllers.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore