Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Migrate sensor thresholds to alarm threshold policies

Alarms

How to configure alarm thresholds and alarm notification policies, mute and acknowledge alarms, and test email notifications sent from EcoStruxure IT Expert

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Expert
  • Configuration
  • Alarms
  • Migrate sensor thresholds to alarm threshold policies
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Alarms
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1991 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Migrate sensor thresholds to alarm threshold policies

Sisko JLehr Sisko
‎2025-02-20 04:48 AM

 

Alarm threshold policies replaced sensor threshold configurations on June 1, 2025.

Go to Alarms > Thresholds to migrate your sensor threshold configurations to threshold policies.

 

 

 

To migrate sensor thresholds to alarm threshold policies:

 

  1. Click Start migration in the banner or go to Alarms > Thresholds and select a threshold.

     

    ITE migrate to threshold policies.png

     

  2. Select target sensors: Filter by device type, manufacturer, model, sensor type, and sensor name, or toggle Target specific device sensors only to manually select one or more sensors. Use the Search field narrow your selection.

     

    ITE migrate to threshold policies select sensors.png

     

  3. Configure threshold: Enter the high and low threshold values that cause warning and critical alarms for numeric sensors. Click the arrow to select units. You can change the values in the fields to visualize the thresholds in the graph. Note: The data shown in the graph are an example, not actual data. 

     

    ITE migrate to threshold policies sensor values.png

     

  4. Configure hysteresis: Hysteresis settings reduce chattering from frequently occurring alarms.

     

    ITE migrate to threshold policies hysteresis.png

     

  5. Summary: View the summary and Save the threshold policy.

     

    Delete old threshold: To avoid generating double alarms, select Continue to delete the old threshold from the system (recommended).

    Otherwise, you can click Keep to keep the old threshold configuration (not recommended).

     

    ITE migrate to threshold policies delete old threshold.png

     

Learn more about Alarm threshold policies in IT Expert

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

Comments
Harikishor_M_G
Harikishor_M_G Cadet
Cadet
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-05-08 10:43 PM

What happens to the existing sensor thresholds configurations, if it is not migrated to alarm threshold policies before 1st June? Doesn't it work or migrate automatically ?? @JLehr 

JLehr
Sisko JLehr Sisko
Sisko
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-05-09 03:55 AM

Hi @Harikishor_M_G,

 

There is no automatic migration. You'll need to migrate sensor thresholds to threshold policies by June 1. Otherwise, you'll have to reconfigure them.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore