We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!
AVEVA Plant SCADA Forum
A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-08-23 06:37 AM . Last Modified: 2019-08-23 07:18 AM
is there a parameter or something else to set on CITECT SCADA (2016 or 2018) which allows to establish the communication between CITECT SCADA and M221 via OFS. the IODeviceInfo stay OFFLINE, while the Device on OFS is ONLINE.
thanks to help
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-08-28 12:35 AM
Hi
We would require more information about your configuration to give a detailed answer, however, the following should give you something to investigate: -
I have attached a white paper which may give you an insight into the communication method between Citect and OFS, it’s based on a M580 and NOT a M221. Therefore only read the information regarding Citect to OFS.
Regards
Rob
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-08-28 07:40 AM
Thanks, Robert
In fact I have no problem to communicate with M340 or M580 through OFS.
As you recommanded, Citect IOServer and OFS Server are running on the same PC.
In addition, the prject was developped by Vijeo Citect 2015, the communication between Vijeo Citect and M221 via OFS was simple and easy.
When I converted the project to CITECT SCADA, the communcation problem was appear.
Then I tried these:
1- Communication CITECT SCADA & M221 without OFS --> OK
2- communication OFS Client M221 via OFS server --> OK , more, the device "M221" on OFS server was ONLINE & GOOD
But no communication between CITECT SCADA and OFS Server (Tag values "BAD"), I tried to verify the state of IODevice, using IODeviceInfo("M221",3) the value remained "16" , witch means The IODevice was OFFLINE.
If, you need more information, i'll try to send you a screen printers next week.
Best regards
Samir
-
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-08-29 01:48 AM
Hi Samir
Unfortunately, I don’t have a M221 and therefore unable to test, however there are still a few things we can try.
Regards
Rob
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-03 08:44 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-02-03 08:44 AM
Hi @NourAutomation,
@RobertSanders helped you in your topic. if his answer solved your problem I kindly invite you to click on “Accept as Solution” so other members can find the same solution through the search bar.
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-11 01:00 PM
communication tag between PLC x SCADA
Is there any way to create a tag that identifies when communication is lost between the clp and scada? The protocol is OPC-UA,
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of