Unable to read data from Huawei SmartLogger 3000B in Power Operation — communication OK but no values

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Unable to read data from Huawei SmartLogger 3000B in Power Operation — communication OK but no values
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
Lt. Commander olivier_vallee
34
Oncom
Commander Oncom
6
BevanWeiss
Spock BevanWeiss
2
RoozeeR
Lt. Commander RoozeeR Lt. Commander
2
View All
Related Products
product field
Schneider Electric
Citect SCADA
product field
Schneider Electric
EcoStruxure™ Building Operation
product field
AVEVA
AVEVA™ Plant SCADA
field url
Schneider Electric
EcoStruxure Power Operation
field url
Schneider Electric
Power Monitoring Expert
Load more

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to AVEVA Plant SCADA Forum
Start a Topic
Solved
NISHANLK25
Crewman NISHANLK25
Crewman

Posted: ‎2025-10-11 07:35 AM

0 Likes
2
118
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-11 07:35 AM

Unable to read data from Huawei SmartLogger 3000B in Power Operation — communication OK but no values

I’m trying to integrate a Huawei SmartLogger 3000B (B02EU) gateway with Schneider Power Operation (EcoStruxure) using Modbus TCP, and while communication is established (connection OK), no actual measurement data is being read (all values show zero).

USERGR12_1-1760191939653.png

 

Here’s the setup and what I’ve tried so far:


Setup

  • Schneider Software: Power Operation (version: 2024)

  • Gateway / MODBUS TCP Server: Huawei SmartLogger 3000B02EU

  • Downstream Device (RS-485 Modbus RTU): Schneider / Third-party energy meters (PM2200)

  • Modbus Chain:
    Power Operation (TCP client) → Huawei SmartLogger (TCP server + RTU master) → RTU meters


What works

  • Network-level TCP communication is successful (no connection errors, port 502 is open).

  • The SmartLogger web interface shows the RTU devices are recognized and mapped under
    Maintenance → Modbus TCP.

  • I have the Huawei SmartLogger Modbus TCP register mapping document (EDOC1100108365

 What doesn’t work

  • When I configure a tag in Power Operation using register address 32261 and 32261 , Data type REAL, etc., but I still get no data (zero) in the system.

  • Modbus polling from Power Operation yields no error responses (timeout or no exception), just no valid values.

  • I suspect the issue is in the mapping / addressing / word order setup.


Configuration I’m using for register 32261 (example Voltage A-N tag in EPO)

Parameter Setting
Register Address 32261
Function Code 3 (Holding Register)
Register Count 2 (32-bit)
Data Type Long (Swapped) / Float (Swapped) — not sure which is correct
Word Swap Enabled / “Swapped”
Slave ID 2
Polling Interval 2000 ms
Protocol ModNet / Modbus TCP


I have also tested via Modbus Poll (TCP) with the same config,

 *Register Address - 32260
 *Data Format - Long AB CD
 *Function - 03 Read Holding Registers (4x)

with above setup I am able to receive a valid numeric value from that Register,

USERGR12_0-1760191807342.png


And I have also tested via EBO - Schneider Building Operation (TCP),

USERGR12_2-1760192422146.png

i also getting data with ,

 *Register Address - 32261
 *Data Format - 32bit unsigned swapped

with above 2 methods I'm able to get Values but it isn't work on EPO


 What I believe might be wrong / need help with

  1. Incorrect data type / word order — maybe it should be Float (Swapped) instead of Long (Swapped)

  2. Device index mapping inside the SmartLogger’s Modbus TCP configuration

  3. Device not forwarded by SmartLogger (mapping not enabled for that RTU to TCP)

  4. Huawei mapping offset / adjustment — maybe 32261 in the documentation needs an offset adjustment

  5. Scale factor / conversion is missing (value is valid, but too small and shows zero after scaling)


What I’m requesting from the community

  • Has anyone successfully integrated a Huawei SmartLogger 3000B with Schneider Power Operation via Modbus TCP?

  • What data type (Long vs Float) and swap / endianness did you use for register 32261 (or similar registers)?

  • Did you have to apply any hotfix / patch in Power Operation to support SmartLogger’s mapping?

  • Any sample configuration (tag setup screenshot, sample mapping file) would be greatly appreciated.

  • Also happy to share log traces / screenshots if someone wants to help deeper.

Thank you in advance for any suggestions or pointers!

Labels
  • Labels:
  • Plant SCADA Runtime
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Next Topic

Accepted Solutions
NISHANLK25
Crewman NISHANLK25
Crewman

Posted: ‎2025-10-15 08:46 PM

0 Likes
0
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 08:46 PM

USERGR12_0-1760585947471.png

I found the solution for this.. you have to put (x4) function code in front of register number, don't forget to put both registers address because it 32bit. then u will get data from one register but keep them both. also set protocol as MODNET30 and put address as power meter Modbus address.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Kien_Mac
Lieutenant JG Kien_Mac Lieutenant JG
Lieutenant JG

Posted: ‎2025-10-14 10:47 PM

0 Likes
0
98
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-14 10:47 PM

Hi UserGR12,
If you are based in Australia, please forward your enquiry to techsupport.pz@schneider-electric.com.
They would be happy to followup with your Power Operations enquiry.
This is a dedicated forum for Plant SCADA.
Thanks.

Kien Mac
Technical Solutions Consultant
Reply

Link copied. Please paste this link to share this article on your social media post.

NISHANLK25
Crewman NISHANLK25
Crewman

Posted: ‎2025-10-15 08:46 PM

0 Likes
0
72
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-15 08:46 PM

USERGR12_0-1760585947471.png

I found the solution for this.. you have to put (x4) function code in front of register number, don't forget to put both registers address because it 32bit. then u will get data from one register but keep them both. also set protocol as MODNET30 and put address as power meter Modbus address.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore