Not able to read modbus data from energy meter

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Not able to read modbus data from energy meter
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
Lt. Commander olivier_vallee
28
Oncom
Commander Oncom
6
BevanWeiss
Spock BevanWeiss
2
RoozeeR
Lt. Commander RoozeeR Lt. Commander
2
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to AVEVA Plant SCADA Forum
MrBong
Ensign MrBong
Ensign

Posted: ‎2024-07-22 04:37 AM

0 Likes
6
1567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-22 04:37 AM

Not able to read modbus data from energy meter

I am having  Elite secure 440 energy meter, I am not getting Modbus data in plant Aveva Scada. I am getting in modscan or modpoll but not in Scada. Please guide further.

 

I am attaching the modbus list of energy meter.

Attachments
Labels
  • Labels:
  • Plant SCADA Studio
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2024-07-23 08:26 PM

0 Likes
0
1543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-23 08:26 PM

Hi @MrBong,

Can you confirm what protocol you are using in Plant SCADA? Is it Modnet (TCP/IP) or Modbus (Serial)?

The most common issue is the Device ID setting, which should be entered into the Plant SCADA, Unit Address field (Plant SCADA Studio > Topology > I/O Devices > Address). This usually defaults to 1.

The other most common issue is relating to the device itself, especially this compact power meters or IEDs is the address range they support. By default the Modnet (and I think Modbus) driver will try to read register 400001 before bringing the unit online. If this address space doesn't exist, the driver won't come online. See the drive help on how to modify this default startup read address.

If you still can't get this worked out, maybe get Wireshark and scan the packets (if TCP/IP) for your Modscan or Modpoll, then compare it to what Plant SCADA is sending on the wire.

If you are still stuck, report back with more info and I will try some more suggestions. Alternatively, you can contact AVEVA Support and get some syslog.dat file and driver reported errors ready so they can troubleshoot it more with you.

Kind regards
Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

MrBong
Ensign MrBong
Ensign

Posted: ‎2024-07-23 10:36 PM

0 Likes
0
1533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-23 10:36 PM

@olivier_vallee It is Modbus TCP/IP and I have entered Device ID correct, which I have configured in multi function meter. I am getting data of L&T WL4410 and WL4420 multifunction meter in Plant Scada. But not getting data of Elite secure 440. Both meter are in one loop.

I have attached the Modbus address list of both energy meter.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2024-07-24 09:40 PM

0 Likes
2
1504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-24 09:40 PM

Hi @MrBong,

Please note that MODNET30 variant is designed to work with TSX Premium and M340 PLCs. This might not be the appropriate variant to communicate with this device. Have you tried setting the protocol to MODNET or one of the other variants like MODNET1?

I'd recommend the following:

1. Using Modscan or Modpoll tool, can you read register 400001?

2. If yes, can you also read 125 contiguous registers in the device? This is how many registers the Modnet driver can attempt to read in one block request. Some smaller devices have non-contiguous address space.

3. Setup a new project, with a single I/O Device and single variable tag. See if this works.

4. If step 3 doesn't work, then use Wireshark to scan the network to see what modbus TCPIP messages the Modscan or Modpoll tools send. Then do the same with your basic AVEVA Plant SCADA and Modnet driver project.

5. Finally if all else fails, set driver logging (see MODNET help for how to do that). Contact AVEVA Support and provide them with the log files and details of your device.

Reply

Link copied. Please paste this link to share this article on your social media post.

MrBong
Ensign MrBong
Ensign

Posted: ‎2024-07-26 01:47 AM

In response to olivier_vallee
0 Likes
1
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-26 01:47 AM

I have tried all variants Modnet but none of them giving data.

1) I am getting data of L&T WL4410 and WL4420 multifunction meter  in Modscan and Modpoll, Which is starting from 40101 and i have put 400100, Then i am getting data in scada. But the elite secure 440 starting address is 40100, Which i am getting modsan & modpoll, but when i doing same process it is not showing data for any parameters.

2) I have done setting up new project also but same issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

MrBong
Ensign MrBong
Ensign

Posted: ‎2024-07-26 09:14 PM

0 Likes
0
1428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-26 09:14 PM

@olivier_vallee Modbus address of device is 40108 for RY volt,40110 for YB volt and 40112 for BR volt. 

What should i assign to get the value in scada?

Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2024-07-28 04:44 PM

In response to MrBong
0 Likes
0
1442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-28 04:44 PM

I recommend you contact SE or AVEVA Customer Support to troubleshoot this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of