Loss of Tags in SCADA After PLC Updates

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Loss of Tags in SCADA After PLC Updates
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
Lt. Commander olivier_vallee
28
Oncom
Commander Oncom
6
BevanWeiss
Spock BevanWeiss
2
RoozeeR
Lt. Commander RoozeeR Lt. Commander
2
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to AVEVA Plant SCADA Forum
Solved
oualid
Crewman oualid
Crewman

Posted: ‎2024-07-23 12:07 PM

0 Likes
5
754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-23 12:07 PM

Loss of Tags in SCADA After PLC Updates

Description:

Hello Support Team,

I am encountering an issue with our DCS system where we are losing tags in our SCADA system after making changes and uploading them to one of our PLCs. Here are the details of our setup and the issue:

System Configuration:

  • OPC Server: Schneider OPC Factory Server
  • SCADA Software: Vijeo Citect 2015
  • Connection: Ethernet
  • PLCs: 5 PLCs connected via Ethernet (PLC1 to PLC5)
  • Machine Setup: The OPC server and SCADA are running on the same machine.

Issue Description:

Whenever I make changes to one of the PLCs (e.g., PLC1), and upload these changes to the PLC three times, we observe that some tags in the SCADA system corresponding to this PLC are lost. This issue is consistent and happens every time we follow this procedure.

Steps to Reproduce:

  1. Make changes to PLC1.
  2. Upload the changes to PLC1.
  3. Repeat the upload process three times.
  4. Observe the loss of some tags in Vijeo Citect 2015 SCADA.
Labels
  • Labels:
  • Communication Drivers
  • Graphics Builder
  • Plant SCADA Runtime
  • Servers - Clients
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2024-07-29 05:47 AM

In response to oualid
0 Likes
1
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-29 05:47 AM

It has been quite some time since I used Unity Pro to program the PLC, but I believe there should be an option to create the data dictionary on build of the PLC program, which also gets stored in the PLC memory. Here is the Schneider FAQ which outlines the steps:

https://www.se.com/sg/en/faqs/FA384523/

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2024-07-24 09:27 PM

1 Like
3
723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-24 09:27 PM

Hi @oualid,

Wow, you have some vintage product versions in production! Any reason why you haven't updated them to take advantage of latest bug fixes and enhancements?

What I can say is that this is a known issue. Basically OFS and the PLC are out of sync when you make changes to the PLC tag database. This was resolved in OFS by allowing it to pre-load the updated Data Dictionary from the PLC before starting the new scan and implementating the PLC changes. 

 

See this forum post for the problem and recommended solution:

https://community.se.com/t5/Modicon-PAC-Forum/OFS-Server-Preloading-on-build-changes-program/td-p/26...

 

Basically upgrade to the latest OFS version 3.63 SP3, tick the options in OFS for "Using Data Dictionary" and "No Communications Break" to ensure there is no comms break between SCADA, OFS and the PLC. Of course if you modify a tag name in the PLC, you would also need to make the corresponding change to the Variable Tag Address to match.

Reply

Link copied. Please paste this link to share this article on your social media post.

oualid
Crewman oualid
Crewman

Posted: ‎2024-07-26 03:10 PM

In response to olivier_vallee
0 Likes
2
688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-26 03:10 PM

Hi @olivier_vallee,

I am no responsable for the updated the product versions and no one here to do that, I would like to do that.
about the OFS options "Using Data Dictionary" and "No Communications Break" are ticked.
I followed the forum post provided from you, I find only the preload on build changes in the PLC project settings \ embedded data settings is not ticked, is that what you meant, about allowing the OFS to pre-load the updated Data Dictionary from the PLC before starting the new scan?


Thank you about your quick response.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2024-07-29 05:47 AM

In response to oualid
0 Likes
1
687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-29 05:47 AM

It has been quite some time since I used Unity Pro to program the PLC, but I believe there should be an option to create the data dictionary on build of the PLC program, which also gets stored in the PLC memory. Here is the Schneider FAQ which outlines the steps:

https://www.se.com/sg/en/faqs/FA384523/

Reply

Link copied. Please paste this link to share this article on your social media post.

oualid
Crewman oualid
Crewman

Posted: ‎2024-12-13 01:42 PM

In response to olivier_vallee
0 Likes
0
439
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-13 01:42 PM

Hi @olivier_vallee, thank you for your time and advice. I resolved the issue by generating a new XVM symbol table file after adding the new tags to the PLC program and replacing the old file with. This allowed the OFS to reconnect with the PLC successfully.

Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2024-12-17 03:07 PM

0 Likes
0
431
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-17 03:07 PM

Thanks for the feedback. Please know that newer versions of OFS are capable of reading the Data Dictionary stored in the PLC (after it is updated) and provide a seamless solution with no interruption to communications or manual exporting files. But I'm glad to hear you are happy with the solution you found.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of