I need to read the PLC I/O data through AVEVA Plant SCADA 2020. The issue is that the PLC program does not assign memory addresses for each I/O point
AVEVA Plant SCADA Forum
A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Select a Country
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • I need to read the PLC I/O data through AVEVA Plant SCADA 2020. The issue is that the PLC program does not assign memory addr...
olivier_vallee
olivier_vallee
38
Oncom
Oncom
6
stuartm
stuartm
2
Modicon M580
Back to AVEVA Plant SCADA Forum
Dilhan
Dilhan
Contributor
Posted: ‎2025-04-07 11:59 PM
4846
I need to read the PLC I/O data through AVEVA Plant SCADA 2020. The issue is that the PLC program does not assign memory addresses for each I/O point. The system uses a Schneider M580 PAC, which is connected to the SCADA via TCP/IP Ethernet.
When I try to add an output like %Q1.1.20 in SCADA, it gives a "Bad I/O" error. I’m not sure how to view the Modbus addresses for each I/O point. Unfortunately, I cannot edit the PLC code because the factory operates 24/7.
Is there a way to connect the I/O directly with SCADA, or any method to monitor or identify the Modbus addresses for each I/O?
  • Plant SCADA Studio
Mnabil
Mnabil Troubleshooter
Troubleshooter
Posted: ‎2025-04-08 10:20 PM
4817
Hello
There are different ways to connect, but I prefer to use OFS approach (OPC software delivered with Plant Scada)
What you will do , export the variables from PLC in XVM format and configure the OFS connection parameters and add the variable file into OFS configuration
Mnabil
Troubleshooter
Posted: ‎2025-04-09 09:20 AM
Can you follow the setting in the attached print screens and you need to add name in PLC Tags
Replies 9
Mnabil
Troubleshooter
4818
Hello
Dilhan
Dilhan
Contributor
Posted: ‎2025-04-08 10:32 PM
@Mnabil I connected it through the OFS tool; the connection was successful, but there were errors when importing tags into Plant SCADA Studio.
Mnabil
Troubleshooter
olivier_vallee
olivier_vallee
Mentor
Posted: ‎2025-04-14 05:19 PM
Hi @Dilhan,
As others have mentioned, to communicate with the M580 with unlocated tags, you will need to use OFS (communications gateway) and the OFSOPC driver from Citect.
The easiest method is to export the tag config to XVM file, and have OFS use that file. Please note that if regular changes are made to the PLC code and tags, it is better option to enable "Tag Dictionary" and "Online Changes" capability in OFS. There is a good "TechNote" on the AVEVA website which walks through all the settings.
Sheshan99
Sheshan99
Explorer
Posted: ‎2025-04-19 04:32 AM
In response to Mnabil
4697
Dear Sir ,
Can you tell me, How can i add the variable into OFS configuration ,And if you have sample XVM it will helpfull me to development.
dnordenberg1
dnordenberg1
Explorer
Posted: ‎2025-04-21 02:03 PM
OFS should be able to read topological addresses but I'm not absolutely sure M580 will let you do that since they are trying to move away from topological addressing. Otherwise you can do a online change and add those IOs as variables, that will not stop the program in any way. Just do a build when connected to the PLC and make sure online change is possible (should say "equal" and "built" at the bottom of the screen before you start adding code. Warning if you do a "build" while not connected you loose the ability to do online change and it will say "not equal att the bottom". Then you have to restore a backup or download the project from PLC to get in "sync" again.
olivier_vallee
olivier_vallee
Mentor
Posted: ‎2025-04-21 06:12 PM
In response to Sheshan99
1
4658
Hi @Sheshan99,
You don't actually add the variable into OFS. But you do specify the variable tag database if "Data Dictionary" is not enabled in the PLC.
So this is a setting on the PLC side, what this does is place a variable tags (and EDT, DDT) library into memory. This is then accessible by remote applications (like OFS).
If you do not have Data Dictionary enabled in the PLC, you must export from Unity Pro (or what ever PLC programming software you have) the Variable Tag database, to an XVM file. But bear in mind that every time you make a change on the PLC, you might have to export this file and update it on your OFS node. This could cause some communications interruptions. So the best and easiest option is to enable Data Dictionary, that way OFS will automatically get the latest variable tag list.
dnordenberg1
dnordenberg1
Explorer
Posted: ‎2025-04-21 10:43 PM
In response to olivier_vallee
I have not used the Plant SCADA OFS (which I understand is built in?) but with the standalone OFS and you can also just type the topological address like %MWxx, %Mxx, %Qxx, %Ixx if the tag list is not fetched via dictionary or imported via XVM.
olivier_vallee
olivier_vallee
Mentor
Posted: ‎2025-04-27 05:36 PM
Hi @dnordenberg1,
The "OFS standalone" is basically the same version that is included with Plant SCADA, I guess it just depends on the version number. The Product feature set is is sized "Large". Latest version is V3.63SP3. The Plant SCADA installs the same version that is available from SE website, but the installer just uses custom serial number and product code to enable the license to make use Plant SCADA license.
It should in theory be possible to use direct addresses in Plant SCADA / OFS.
The OFSOPC driver in Plant SCADA communicates with OFS via OPC DA protocol.
It is best to use the tag name defined in the PLC (via Data Dictionary or XVM) in the communications definition.