A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-07 11:59 PM
I need to read the PLC I/O data through AVEVA Plant SCADA 2020. The issue is that the PLC program does not assign memory addresses for each I/O point. The system uses a Schneider M580 PAC, which is connected to the SCADA via TCP/IP Ethernet.
When I try to add an output like %Q1.1.20
in SCADA, it gives a "Bad I/O" error. I’m not sure how to view the Modbus addresses for each I/O point. Unfortunately, I cannot edit the PLC code because the factory operates 24/7.
Is there a way to connect the I/O directly with SCADA, or any method to monitor or identify the Modbus addresses for each I/O?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-08 10:20 PM
Hello
There are different ways to connect, but I prefer to use OFS approach (OPC software delivered with Plant Scada)
What you will do , export the variables from PLC in XVM format and configure the OFS connection parameters and add the variable file into OFS configuration
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-09 09:20 AM
Can you follow the setting in the attached print screens and you need to add name in PLC Tags
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-08 10:20 PM
Hello
There are different ways to connect, but I prefer to use OFS approach (OPC software delivered with Plant Scada)
What you will do , export the variables from PLC in XVM format and configure the OFS connection parameters and add the variable file into OFS configuration
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-08 10:32 PM
@Mnabil I connected it through the OFS tool; the connection was successful, but there were errors when importing tags into Plant SCADA Studio.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-14 05:19 PM
Hi @Dilhan,
As others have mentioned, to communicate with the M580 with unlocated tags, you will need to use OFS (communications gateway) and the OFSOPC driver from Citect.
The easiest method is to export the tag config to XVM file, and have OFS use that file. Please note that if regular changes are made to the PLC code and tags, it is better option to enable "Tag Dictionary" and "Online Changes" capability in OFS. There is a good "TechNote" on the AVEVA website which walks through all the settings.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-19 04:32 AM
Dear Sir ,
Can you tell me, How can i add the variable into OFS configuration ,And if you have sample XVM it will helpfull me to development.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-21 02:03 PM
OFS should be able to read topological addresses but I'm not absolutely sure M580 will let you do that since they are trying to move away from topological addressing. Otherwise you can do a online change and add those IOs as variables, that will not stop the program in any way. Just do a build when connected to the PLC and make sure online change is possible (should say "equal" and "built" at the bottom of the screen before you start adding code. Warning if you do a "build" while not connected you loose the ability to do online change and it will say "not equal att the bottom". Then you have to restore a backup or download the project from PLC to get in "sync" again.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-21 06:12 PM
Hi @Sheshan99,
You don't actually add the variable into OFS. But you do specify the variable tag database if "Data Dictionary" is not enabled in the PLC.
So this is a setting on the PLC side, what this does is place a variable tags (and EDT, DDT) library into memory. This is then accessible by remote applications (like OFS).
If you do not have Data Dictionary enabled in the PLC, you must export from Unity Pro (or what ever PLC programming software you have) the Variable Tag database, to an XVM file. But bear in mind that every time you make a change on the PLC, you might have to export this file and update it on your OFS node. This could cause some communications interruptions. So the best and easiest option is to enable Data Dictionary, that way OFS will automatically get the latest variable tag list.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-21 10:43 PM
I have not used the Plant SCADA OFS (which I understand is built in?) but with the standalone OFS and you can also just type the topological address like %MWxx, %Mxx, %Qxx, %Ixx if the tag list is not fetched via dictionary or imported via XVM.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-27 05:36 PM
Hi @dnordenberg1,
The "OFS standalone" is basically the same version that is included with Plant SCADA, I guess it just depends on the version number. The Product feature set is is sized "Large". Latest version is V3.63SP3. The Plant SCADA installs the same version that is available from SE website, but the installer just uses custom serial number and product code to enable the license to make use Plant SCADA license.
It should in theory be possible to use direct addresses in Plant SCADA / OFS.
The OFSOPC driver in Plant SCADA communicates with OFS via OPC DA protocol.
It is best to use the tag name defined in the PLC (via Data Dictionary or XVM) in the communications definition.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of