Help :About AVEVA PLANT SCADA 2023 R2 DRIVER

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Help :About AVEVA PLANT SCADA 2023 R2 DRIVER
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
Lt. Commander olivier_vallee
34
Oncom
Commander Oncom
6
BevanWeiss
Spock BevanWeiss
2
RoozeeR
Lt. Commander RoozeeR Lt. Commander
2
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to AVEVA Plant SCADA Forum
Start a Topic
Solved
yuzl
Crewman yuzl
Crewman

Posted: ‎2025-04-25 08:21 PM

0 Likes
5
1064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-25 08:21 PM

Help :About AVEVA PLANT SCADA 2023 R2 DRIVER

Does AVEVA PLANT SCADA 2023 R2 have an OPC/UA SERVER DRIVER and how to use it.

Labels
  • Labels:
  • Plant SCADA Anywhere
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2025-05-06 08:21 PM

In response to yuzl
0 Likes
2
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 08:21 PM

Hi @yuzl ,

Plant SCADA 2023 R2 does certainly have a OPCUA Server, which is part of the "AVEVA Connectivity Service" that runs on the machine. It is optional to install, so if it isn't present, you may need to run the installer to make sure it is added and installed properly.

The first step is to run Configurator, to define the port number, whether encryption is enabled or anonymous access is allowed.

olivier_vallee_0-1746587750590.png

See the help topic for more details:

https://docs.aveva.com/bundle/plant-scada/page/1037376.html

 

You'll need to copy the OPCUA Server certificate to the client machine if using encrypted communications.

Let me know how you go and if you have any specific questions.

Kind regards

Olivier

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2025-05-04 09:05 PM

0 Likes
4
1027
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-04 09:05 PM

Hi @yuzl ,

Yes, Plant SCADA 2023 R2 does have a OPCUA Client driver. Please see the following help for more details:

https://docs.aveva.com/bundle/plant-scada/page/843695.html

It is a bit more involved in terms of setup and configuration (especially if setting up secure connection). 

Let me know how you go and if you have any specific questions.

Kind regards

Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

yuzl
Crewman yuzl
Crewman

Posted: ‎2025-05-05 05:22 PM

In response to olivier_vallee
0 Likes
3
1006
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-05 05:22 PM

Hi @olivier_vallee ,

Thank you for your response. It appears that there may be a slight inaccuracy in my original question. I am already familiar with the OPC UA Client driver. What I aim to achieve is configuring Plant SCADA 2023 R2 as an OPC UA Server, thereby enabling communication between the OPC UA Client and the server.

Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2025-05-06 08:21 PM

In response to yuzl
0 Likes
2
1002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 08:21 PM

Hi @yuzl ,

Plant SCADA 2023 R2 does certainly have a OPCUA Server, which is part of the "AVEVA Connectivity Service" that runs on the machine. It is optional to install, so if it isn't present, you may need to run the installer to make sure it is added and installed properly.

The first step is to run Configurator, to define the port number, whether encryption is enabled or anonymous access is allowed.

olivier_vallee_0-1746587750590.png

See the help topic for more details:

https://docs.aveva.com/bundle/plant-scada/page/1037376.html

 

You'll need to copy the OPCUA Server certificate to the client machine if using encrypted communications.

Let me know how you go and if you have any specific questions.

Kind regards

Olivier

 

Reply

Link copied. Please paste this link to share this article on your social media post.

yuzl
Crewman yuzl
Crewman

Posted: ‎2025-05-06 08:44 PM

In response to olivier_vallee
0 Likes
1
980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-06 08:44 PM

Hi @olivier_vallee , Thank you. I have already addressed the task and successfully verified the functionality of the OPC UA Server. Additionally, could you please confirm whether the OPC Server supports hot standby? For my project, which involves a hot standby server and standalone client, should I consider implementing a hot standby mechanism at the OPC UA Client level? Kind regards Yuzl
Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2025-05-07 04:09 PM . Last Modified: ‎2025-05-07 04:09 PM

In response to yuzl
0 Likes
0
970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-07 04:09 PM . Last Modified: ‎2025-05-07 04:09 PM

Hi @yuzl,

The Plant SCADA OPC UA Server does not support hot standby capabilities. It is stand alone. But you can install and setup multiple OPC UA Server's in your system, each on different host machines. If your OPC UA Client supports some redundancy mechanism, and you can provide the End Point URL for each Server that is providing data, it should work well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore