Citect 2018 R2 OPC-DA server connection issue with client

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Citect 2018 R2 OPC-DA server connection issue with client
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
Commander olivier_vallee
34
Oncom
Commander Oncom
6
Kien_Mac
Lieutenant JG Kien_Mac Lieutenant JG
2
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
Citect SCADA

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to AVEVA Plant SCADA Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2022-08-31 07:10 PM

1 Like
1
4612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-31 07:10 PM

Citect 2018 R2 OPC-DA server connection issue with client

Hi Dears,

 

I have an issue making a connection between PI Interface and Scada OPC-DA. PI Interface is on another VM and trying to make a connection to the Scada OPC-DA server. I have configured the DCOM setup as per OSI PI and Citect documentation at both Scada and PI Interface VMs. OPC DA has been enabled in the Scada server and it's running in the run-time manager. The DCOM access for Citect OPC DA name is AVEVA SCADA OPC DA Server. There are 3 options to allow the users to run the OPC-DA as the interactive user, the launching user and this user. When I select the interactive user (the person who already is logged in to the Scada server) by any OPC explorer like Matricon or OPCExpert I can connect to the OPC-DA and browse the data locally and remotely but as soon as I change the access to this user and put the service account user and pass in and tries to connect by PI Interface for OPC-DA which runs under the same service account the OPC server denied the connection. I have added the service account to be a local administrator in the Scada servers and also to my computer com security. It has launch and activation permission. It looks like Citect 2018 R2 doesn't trust to any other users unless they are interactive users but this doesn't make any sense for me as you are not going to login to the I/O servers forever. I think something is running in the background which doesn't allow OPC server to trust to any other user even if they have full access and permissions in the I/O servers.

 

I have checked netstat command in the CMD to monitor any TCP connections between PI Interfaces and I/O servers. There was established TCP Port 135 and 50085 between primary interface and secondary I/O servers when the successful connection to OPC server established but again this was the interactive user. When it wasn't interactive user the primary I/O server port 135 and 50085 was on Time-Wait. This shows the DCOM connection was successful but OPC was unresponsive. Please let me know if anyone had the same issue which I'm currently facing with the Citect 2018 R2.

 

This is a blocker for our historian project and I need to resolve it. Any alternative solution can be considerable. Your prompt response would be highly appreciated.

 

Best Regards,

Rasoul

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Kien_Mac
Lieutenant JG Kien_Mac Lieutenant JG
Lieutenant JG

Posted: ‎2022-09-22 05:30 PM

0 Likes
0
4518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-22 05:30 PM

Hi Rasoul,

This appears to be an issue that requires our Global Customer Support Team to help. I'd like to suggest to reach out to the support team to assist and troubleshoot in more detail.

DCOM issues can be very tricky. Some suggestions would be to run the Citect Runtime Manager, Service Log On from 'Local System account' to 'Administrator'? I remember that the Local System account is a really locked down Windows account, which is important for security, but also becomes a problem for DCOM and network enabled applications. You may need to reach out to Microsoft or the OPC foundation for guidance on securing the application while still enabling access to network resources and DCOM.

You may also be running into problems with [OpcDaServer]AutoStartByClient=1.


In the meantime, some links that might help.

https://www.youtube.com/watch?v=silTnP4a8do

https://docs.osisoft.com/search
https://docs.osisoft.com/bundle/pi-interface-for-opc-da/page/related-tools-for-pi-interface-for-opc-...

https://pisquare.osisoft.com/s/question/0D58W00007t92O0SAI/citect-interface-firewall-rule-requiremen...
Kien Mac
Technical Solutions Consultant
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore