Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

what is the proper way to connect the RCCB to the UPS.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • what is the proper way to connect the RCCB to the UPS.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

0 Likes
11
14094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

what is the proper way to connect the RCCB to the UPS.

Hi all

I need your expert advice, what is the proper way to connect the RCCB to the UPS, coz im ask some supplier of RCCB they have defferent version on how to install the RCCB.
They told me that from:
1. Main Supply -> RCCB -> UPS -> Load or/
2. Main Supply -> UPS -> RCCB -> Load
I really dont know what is the proper way, BTW the RCCB rating is 30mA and it should be connected/ install to the server rack...

Need you advice

Thanks to all

Message was edited by: black Aces

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

The wall receptacle GFI is not available in my country, I've never seen one here nor those portable ones available in the US. Where you usually see GFCIs installed here is in the cicuit breaker panels, one for all circuits or one or more for circuits feeding external areas, areas where water is close to the circuits that people tend to use electrical appliances, and in bathrooms. In my house I have one three phase + neutral RCD that protects all circuits and we never had any problem with it...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

0 Likes
0
14090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

so if you say that the RCCb is connected before the UPS, FYI the rating of the RCCB is 30mA then what if my UPS input current rating above/ or 5Amps, basically the RCCB will keep on triping right?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

0 Likes
0
14091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

No, it's not gonna keep tripping because of the 30mA rating, you're making some confusions here.

The rating given in miliamps, mA, is the number at which the RCCB will trip in case electricity leaks to earth, or ground as the americans say. If a person get shocked or there is a fault inside an equipment that causes it to leak current to earth, the RCCB will trip, thus protecting the electrical installation itself and mainly, the user of that piece of equipment.

If you look at the data written in front of RCDs you'll see its nominal amperage rating, which can be 10A, 25A, 40A, 63A, 80A, 100A, you see its sensitivity rating (the amount of leakage current that make the RCD trip) given in mA, 30mA, 100mA, 300mA, 500mA. There are also other stuff written there like the maximum current that the device is capable of handling when it turns itself off without breaking the device like, 6000A, 10000A and sometimes the schematics of how you plug the device comes printed in front of it as well along with other information like the voltage rating, etc.

-------------

Let me correct something. An RCCB DO NOT work as a normal circuit breaker as I said before, it works only as a leakage current protector or earth fault protector. An RCBO is the one that works as a normal circuit breaker and an earth (ground) fault detector on the same product.

The "ln" rating, or the nominal current of an RCCB only indicates the maximum continous current the device can handle, but it won't trip in the case of short circuit or overload, it will only trip on leakage current faults!

An RCBO trips if one of the three problems occur: Overload, Shot-Circuit and Leakage current.

Message was edited by: rau

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

0 Likes
0
14092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

Dear friends,

Could you pls share your comments on the RCCB-Connected in series-what happens?-?Connected in Parallel-what happens?

Share your comments pls!!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

0 Likes
0
14089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

i am not sure what RCCB is? ๐Ÿ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

0 Likes
0
14089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

RCCB is basically the "american" GFCI.

RCCB is the short for: Residual Current Circuit Breaker it works as a GFCI and a normal Circuit Breaker in one product. It's one of the many types of RCD - Residual Current Devices. In Brazil we call it DDR or IDR.

The RCCB should be installed before the UPS in the Circuit Breaker panel also known as "consumer unit" in the UK.

An UPS should never make RCDs trip, if it causes it to trip, it means the leakage current inside the UPS is very high and something is not working properly.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

0 Likes
0
14089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

oh ok. thanks rau!

i know we have an article here on GFCI.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

0 Likes
0
14091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:19 AM

The wall receptacle GFI is not available in my country, I've never seen one here nor those portable ones available in the US. Where you usually see GFCIs installed here is in the cicuit breaker panels, one for all circuits or one or more for circuits feeding external areas, areas where water is close to the circuits that people tend to use electrical appliances, and in bathrooms. In my house I have one three phase + neutral RCD that protects all circuits and we never had any problem with it...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

0 Likes
0
14091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

so if you say that the RCCb is connected before the UPS, FYI the rating of the RCCB is 30mA then what if my UPS input current rating above/ or 5Amps, basically the RCCB will keep on triping right?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

0 Likes
0
14092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

No, it's not gonna keep tripping because of the 30mA rating, you're making some confusions here.

The rating given in miliamps, mA, is the number at which the RCCB will trip in case electricity leaks to earth, or ground as the americans say. If a person get shocked or there is a fault inside an equipment that causes it to leak current to earth, the RCCB will trip, thus protecting the electrical installation itself and mainly, the user of that piece of equipment.

If you look at the data written in front of RCDs you'll see its nominal amperage rating, which can be 10A, 25A, 40A, 63A, 80A, 100A, you see its sensitivity rating (the amount of leakage current that make the RCD trip) given in mA, 30mA, 100mA, 300mA, 500mA. There are also other stuff written there like the maximum current that the device is capable of handling when it turns itself off without breaking the device like, 6000A, 10000A and sometimes the schematics of how you plug the device comes printed in front of it as well along with other information like the voltage rating, etc.

-------------

Let me correct something. An RCCB DO NOT work as a normal circuit breaker as I said before, it works only as a leakage current protector or earth fault protector. An RCBO is the one that works as a normal circuit breaker and an earth (ground) fault detector on the same product.

The "ln" rating, or the nominal current of an RCCB only indicates the maximum continous current the device can handle, but it won't trip in the case of short circuit or overload, it will only trip on leakage current faults!

An RCBO trips if one of the three problems occur: Overload, Shot-Circuit and Leakage current.

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

0 Likes
0
14092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

ah okies, thank you Rau your info is a big help for those people dont have much knowldge like me about this things....:-)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

0 Likes
0
14093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

Dear friends,

Could you pls share your comments on the RCCB-Connected in series-what happens?-?Connected in Parallel-what happens?

Share your comments pls!!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

0 Likes
0
14092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 07:59 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

How is an MCB Connected? In series or parallel?

In series-what happens?

In parallel-what happens?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: โ€Ž2021-06-29 08:00 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

0 Likes
0
14091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 08:00 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

you want them in parallel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-29 08:00 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

0 Likes
0
14091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-29 08:00 PM . Last Modified: โ€Ž2024-03-21 01:18 AM

will as per advise we connect the RCCB in series ( a ground conductor ), we found out also that there's nothing wrong with the UPS, it more on the balancing the mains supply.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore