single battery
  • single battery
2150
127
Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:47 PM
633
single battery
Hi. just wondering if i could use just 1 battery in a 2 battery chassis.
ok. thank you. i will maybe try to trade this for a single battery unit.
I doubt it.  The two battery systems I've seen have the batteries in series so if you removed one then your single battery would only provide half the volts.  Now if the batteries were in parallel (not sure if its done that way; I've not seen it.) then you might get away with it at the expense of a serious cut to capacity.  The results could be worse if the single battery couldn't provide the needed current.  Likely result is the AV rating of the UPS would drop along with the usable time on battery.  YMMV.