Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

shut down computer, not UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • shut down computer, not UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
ND
ND
Explorer

Posted: ‎2023-11-16 07:47 AM

0 Likes
4
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-16 07:47 AM

shut down computer, not UPS

I've recently bought an 850G2 unit, primarily to ensure my fibre broadband + VoIP phone will carry on through a tempory power glitch (not unuaual here to ahve power drop out for a couple of seconds), and continue running for a while in the event of a more extended power cut. I also want to have a small desktop computer hibernate if power drops out for more than a minute, both to avoid system corruption and also to minimise lost work. 

 

Using Powerchute serial software, I'm able to get the computer to shut down, but (a) I can't see how to get the computer to hibernate instead; and, (b) after the computer shuts down, the other equipment connected to the UPS lose power. How do I work found these two issues, please? Is the only solution for me to get an additional small UPS solely to keep the PC running long enough to hibernate or shut down cleanly?

Labels
  • Labels:
  • Home & Office - UPS & Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Teken
Teken
Champion

Posted: ‎2024-02-07 11:44 AM

0 Likes
2
2355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-07 11:44 AM

The UPS has two outputs (Surge Only) and Battery Backup so confirm the other appliances are connected to the correct outlets. As it relates to your computer system, a graceful shut down is the correct method to protect the hardware and its data.

 

The Windows hibernating mode is intended to save power while also speeding up the computer to a working state vs a cold boot. A computer system left in hibernating mode will lose or see data corruption. As the system is literally still running on reduced power. 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

ND
ND
Explorer

Posted: ‎2024-02-21 03:54 AM

In response to Teken
0 Likes
1
2317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-21 03:54 AM

Thanks for the reply. First, you a wrong about Windows hibernation; on Windows 10 and earlier, hibernation meant a complete power-down, but keeping info on disk so everything could resume when things powered back up. You could even remove the battery on a laptop, or disconnect a desktop computer from the mains supply, and state was recovered when things back up. So, hibernation is a sensible option when told by an UPS that power is going away. With Windows 11, Microsoft is encouraging people just to use the sleep mode (which, as you describe, relies on power being maintained), but the true hibernation mode option is still there - just well hidden.

 

Secondly, you have made the simplistic assumption that everything attached to the battery-backed circuit is for use only by the desktop computer. I want the computer to shut down in an orderly manner when the mains power is lost, but I don't want to shut down the router, for example, nor the VOIP adapter; that way, laptops, tablets and phones can carry on using the internet via WiFi for a while, and my 'landline' still works - so I can report the problem with the electricity supply. If the only things being powered by the battery long-term are the router and phone, I'm hoping I should be able to maintain connectivity for a few hours. Is there any way I can set up the desktop computer and UPS so that then the power goes (a) the computer gets a signal which it uses to power down gracefully, and (b) all the devices connected to the battery-protected sockets on the UPS (including the computer) remain powered until the battery dies? I suppose I could do away with using the USB port and instead connect, say, a raspberry pi to one of the unprotected sockets, and have something on the computer that monitors this via pings, ... but this adds complexity!

Reply

Link copied. Please paste this link to share this article on your social media post.

ND
ND
Explorer

Posted: ‎2024-02-22 09:24 AM

0 Likes
0
2304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-22 09:24 AM

(for clarity, I would like to add that I've recently moved from an FTTC internet connection to direct fibre (FTTP), and no longer have a telephone service via copper wire - so the VoIP 'landline' depends on the router working in the event of a power cut, especially as the mobile signal around here is not reliable: the last power cut took out the local masts! Hence the importance of a battery backup for the router, and I was hoping that it would also keep the desktop computer going long enough for a graceful shutdown or hibernation.)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2024-02-22 11:24 AM

In response to ND
0 Likes
0
2314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-22 11:24 AM

@ND 

 

You can configure PowerChute to run a command file after UPS as run on battery for X time that will tell the OS to hibernate. 

 

First set the time on battery threshold. Below I set the threshold to 5 minutes

BillP_0-1708628962871.png

Next Change the shutdown setting to At runtime limit and set that threshold.

BillP_1-1708629051786.png

Next write a command file to hibernate the OS. The command file can be a .bat or .cmd and must be stored in C:\Program Files\APC\PowerChute Serial Shutdown\agent\cmdfiles

 

Comand file contect:

 

powercfg -h on
timeout /t 60
shutdown /h

 

The file will enable hibernation wait 1 minute and the hibernate to OS.

Next within PowerChute configure the command file to be triggered when time on battery as been exceeded.

BillP_2-1708629439597.png

 

In my example the UPS will run on battery for 5 minutes and then PowerChute will trigger the command file to hibernate the OS. The UPS will remain providing output until it reaches low battery.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore