Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84254members
353353posts

scheduled start up and shut down

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
Prashant_apc
Cadet
0 Likes
1
76

scheduled start up and shut down

This was originally posted on APC forums on 9/17/2008


Hi everyone
Can I schedule the start and stop of the power supply to the appliances like modem etc. attached to apc back ups 650.
Thanx in advance


Accepted Solutions
TheNotoriousKMP_apc
Sisko
Sisko
0 Likes
0
76

Re: scheduled start up and shut down

This was originally posted on APC forums on 9/17/2008


Hi,

There's no software or device that's going to be able to control individual power on of devices attached to the UPS.

You would need a switched rack PDU to toggle power to a specific outlet, but nothing in terms of turning the device on with power already present.

See Answer In Context

1 Reply 1
TheNotoriousKMP_apc
Sisko
Sisko
0 Likes
0
77

Re: scheduled start up and shut down

This was originally posted on APC forums on 9/17/2008


Hi,

There's no software or device that's going to be able to control individual power on of devices attached to the UPS.

You would need a switched rack PDU to toggle power to a specific outlet, but nothing in terms of turning the device on with power already present.