Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

"Unexpected Shutdown" reported even though it was (allegedly) managed.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • "Unexpected Shutdown" reported even though it was (allegedly) managed.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

0 Likes
3
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

"Unexpected Shutdown" reported even though it was (allegedly) managed.

Just want to see if this is normal.

I have PowerChute set to preseve battery power and initiate a shutdown after 1 minuted on battery. Client had a blackout today and PowerChute software reports it did a manged shutdown today at the corresponding time of blackout. PowerChute reports the server was on battery for 1 min 21 secs and user reports that the server was on for about 3 mins before fully turning off.

All that makes sense to me. The software report of 1 min 21secs on battery makes sense as it would only be able to track time before the APC service was shutdown as part of the managed shutdown. The total on time of about 3 mins also makes sense as ~2 mins to shutoff the server (after the command was given) is about right.

However, when the server came back up, it had the computer was unexpectdly shutoff "tell me why" bit that server 2003 has in cases of unexpected shutdown. While I have, of course, seen this message when the power went out without an UPS attached to it, I was wondering if it is normal for it to still ask for a shutdown reason if it was successfully shutdown via the PowerChute software.

Thanks all for any insight you can shed on this.

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:21 AM

0 Likes
0
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:21 AM

no APC software adds anything to the event tracker as far as i know. 😕

if you want i can test it out to be sure though.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

0 Likes
0
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

i believe it is. if you havent disabled that "unexpected shutdown" reasoning dialog box, powerchute does not have the ability to add anything into this box.

is this powerchute personal edition or business edition?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:21 AM

0 Likes
0
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:21 AM

Thank you for the response.

It's personal edition and I suspected that Server was going to gripe because it did not get a reason. Nice to have some coroboration on that suspicion. I am very happy, though, that it looks like PowerChute is able to force it past the "reason point" and get it shut off which is just fine with me.

It didn't even occur to me to shutdown event tracker though, thanks for mentioning that. Does bus. edition have the ability to supply a reason though? I have never played around with that edition though I've heard that it is a good bit limited than PE. I have to say that with PE combined with the newer and somewhat higher end models, I am impressed with the functionality (ability to to do on-demand self test etc...).

Thanks again for the response and please feel free to add anything.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:21 AM

0 Likes
0
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:21 AM

no APC software adds anything to the event tracker as far as i know. 😕

if you want i can test it out to be sure though.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore