Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

min & max line voltage on PCBE version 127.0.0.1

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • min & max line voltage on PCBE version 127.0.0.1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

0 Likes
13
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

min & max line voltage on PCBE version 127.0.0.1

Hi all, brand newbie here with a question relating to an SUA750i using PCBE version 127.0.0.1 on windows XP.....

In the log (screen dump attached) there are 2 columns for min and max line voltage which are and have always been "N/A",
I have ticked the relevant sections in the configure log page - also attached

any ideas appreciated
thanks

Attachments
Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

Right, it's a proprietary pin-out. I don't have any diagrams but I bet Google does. 😉

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

Hi all, brand newbie here with a question relating to an SUA750i using PCBE version 127.0.0.1 on windows XP.....

In the log (screen dump attached) there are 2 columns for min and max line voltage which are and have always been "N/A",
I have ticked the relevant sections in the configure log page - also attached

any ideas appreciated
thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

Hi and thanks for the prompt reply...although it's not what I wanted to hear.

So, by using powerchute with, say, Yahoo webmail I cannot use the email facility for any alerts and now, because by default it uses USB to communicate with the PC I also cannot record the highest & lowest line voltages......hmmmmm.....not very good is it ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

yes i understand. but this is where you can post so that APC can hear your complaints and can improve the product.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

buzz....I could use the serial lead .....but my PC doesn't have a serial port and I can't justify fitting one just for that

not being able to use USB does seem rather a backward step though....what is the reasoning behind not being able to use USB....surely it is only a serial comms port, albeit a very fast one

Message was edited by: davidwf

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

You could always use the serial cable instead if you must have those values. They aren't crucial; PowerChute will still serve the purpose of shutting down your computer in the event of an outage (or a number of other events), and record all of the other data, so I suspect the min/max voltages don't really make or break the software. But yeah, that's a limitation of using USB.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

Yeah, you're not the first person to point out serial is outdated, also not the last I suspect. 😉 Though it's not that you can't use USB... USB just doesn't record those values. I honestly am not sure why.

How about a serial to USB adapter? Cheaper than buying a card just for a serial port anyway...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:50 PM . Last Modified: ‎2024-03-20 06:03 AM

would that work ?....it will still be using USB....

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

It's the USB on the UPS, not your computer, so you can use the serial cable and it will read the voltages, and then stick the adapter for USB on the end and it'll be fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

Ah right, I see now.......pity APC tech don't know that....they are still trying to figure out why it isn't working !!!...I will let them sweat a bit more before I tell them

Did I read somewhere that the "serial" port does not use true serial connections.....anybody got a diagram with the pinouts so I can make the correct lead ?

Thanks all

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
voidstar_apc
Contributor

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

It's also somewhat described in [this APC knowledgebase article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1481].

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

APC customer support kindly sent me a serial lead which, with the aid of a serial to USB adapter (I don't have any serial ports) is now reporting the voltages correctly ! 🙂

They are adamant however that a USB lead should do likewise so they are sending me one of those as well......will report back as & when

Thanks for your replies and help so far

D

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

0 Likes
0
3419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

Well well, the "new and correct" USB lead arrived today - which appears to be a bog standard USB lead with no electronics or anything in it.
I un-installed and re-installed everything again and, as before it does NOT output the max & min line voltages...just like you all said in the earlier posts !!!

I have "advised" APC technical about this and also pointed out that I found the answer (on THEIR website) via this user forum.

So, I will continue to use the serial port connected via a USB to serial dongle as I don't have any proper serial ports and it all seems to work OK.

Thanks again to all who offered help
DF

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

0 Likes
0
3420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:51 PM . Last Modified: ‎2024-03-20 06:02 AM

Right, it's a proprietary pin-out. I don't have any diagrams but I bet Google does. 😉

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore