last transfer to battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • last transfer to battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

0 Likes
7
2489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

last transfer to battery

Hi, I usually consider myself a pretty good googler, but info at any respectable level of detail seems to be missing on the whole of the internet for my Smart-UPS 2200.  Even the users manual reads like a set of reminder notes for the people who built it.  The manual directs you to the CD, where you find, of all things, the manual (Gee, thanks).

That's the bigger problem that I'd be happy to have any advice about (a structured, detailed document, anyone?)

Now on to the specific question . . .

The local power utility got around to testing my UPS before I did.  We lost power in the few days after I first plugged everything in, before I got around to installing power-chute and/or any other management utility.  The good news is that the battery seems to have done its job, and my server is fine.   But I am confused as to why I still see "Last Transfer: Test Ended" on the little built-in LCD console menu (because that is all I have to work with for now).  Previously this made sense; it was brand new, and the most recent transfer was probably during the factory test before shipping.  I know we lost power yesterday, and I know the UPS transferred to battery because my jobs are still happily chugging away oblivious to their interim peril.

Does the UPS self test after each event?  How can I get detailed information (times, cause: black-out vs surge)?

Thanks for any help!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • documentation
  • lcd_console
  • transfer
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

Yes. I just verified - lowest number event is the newest.

I suppose there may be a few types of events (or even a bug) that causes the last transfer reason perhaps to not update properly. I just ran into that type of issue on another type of UPS where the last transfer reason did not update properly.

Anyway, PowerChute only has its own log that populates when the service is running on a computer. However, the management card (AP9630/31) does have the capability to show those logs that you see on the front LCD with some type of time next to it. I say "some type of time" since its in milliseconds and you'd need to convert it. See below from my SMX1000. I believe the UPS stores these on its own like you're seeing so the management card could display them. I don't see them being more helpful than what you can see on the UPS itself.

1319_%242392E7C330C06619.jpg

On this UPS, my last transfer reason says unknown.

Anyway, a site wiring fault is explained here (What does the Site Wiring Fault Indicator LED on my UPS/Surge Arrestor represent? | FAQs | Schneider...) so one of these conditions must be true or was at some point. It is something you should look into. Apparently, since these UPSs have the front display, there is no site wiring fault LED on the back now, like most of our other UPSs of this size and smaller.

Lastly, can you tell me the firmware version from the About menu on the LCD? Something like UPS 08.1 ,etc - we can see if its up to date and maybe upgrade it since you just installed it to verify latest firmware? Not sure its going to fix anything but if you'd like to be up to date, I figured I could help you with that.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

Hello.

The UPS only does its self test (by default) when you turn it on and every 14 days (which you can also change). Is it possible the UPS was turned off/on after the event or it did its automatic self test in between?

For any detailed logs for date and time, you'd need to have either the Network Management Card installed (which at least if it was in the UPS, you could configure it and check the log after the fact) or PowerChute Business Edition agent service running via USB or serial as you also mentioned. The UPS itself can only hold those logs you see on the LCD (last 10 transfer reasons or last 10 faults) and they do not show any detailed data via that LCD. I don't think you'll be able to get any more detailed data for this one unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

Thanks for your help, Angela.  I'm glad to have you confirm that the information that I do have means what I think it should mean.  Going with that, the only explanation would be that the UPS self-tested (coincidentally) since the incident.  Only two people have access, and neither of us touched the UPS.

However, I found the "Logs" section under the "Advanced Menus" and I can now see the last 10 events.  "Xfer Events" 1 and 2 are:

1 "Acceptable Input"

2 "Distorted Input"

The remaining events are all "Test Ended"--"Self Test" pairs (4 pairs = 8 entries).  There are no details, but I gather you read the lowest numbered entry as the most recent (otherwise the pairs don't make sense).  This seems to contradict the "Last Transfer" entry under the "Status" menu, which caused me to write.  Since there are no dates, I'm still unsure.  Will those details be viewable when install power-chute and connect via USB?  (I do not have a Network Management Card.)

Also, should I be concerned that there are 10 entries under "Fault Event" and they all say "Site Wiring"?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

0 Likes
0
2489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

Yes. I just verified - lowest number event is the newest.

I suppose there may be a few types of events (or even a bug) that causes the last transfer reason perhaps to not update properly. I just ran into that type of issue on another type of UPS where the last transfer reason did not update properly.

Anyway, PowerChute only has its own log that populates when the service is running on a computer. However, the management card (AP9630/31) does have the capability to show those logs that you see on the front LCD with some type of time next to it. I say "some type of time" since its in milliseconds and you'd need to convert it. See below from my SMX1000. I believe the UPS stores these on its own like you're seeing so the management card could display them. I don't see them being more helpful than what you can see on the UPS itself.

1319_%242392E7C330C06619.jpg

On this UPS, my last transfer reason says unknown.

Anyway, a site wiring fault is explained here (What does the Site Wiring Fault Indicator LED on my UPS/Surge Arrestor represent? | FAQs | Schneider...) so one of these conditions must be true or was at some point. It is something you should look into. Apparently, since these UPSs have the front display, there is no site wiring fault LED on the back now, like most of our other UPSs of this size and smaller.

Lastly, can you tell me the firmware version from the About menu on the LCD? Something like UPS 08.1 ,etc - we can see if its up to date and maybe upgrade it since you just installed it to verify latest firmware? Not sure its going to fix anything but if you'd like to be up to date, I figured I could help you with that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

Ok, it's not worth it to go on a crusade to find out exactly what the UPS thinks happened.  Mostly I was using this as an opportunity to make sure I understood, in general, what it is trying to tell me.  If there is a known issue there, it's not a rabbit hole worth exploring.  I will install PowerChute in the next couple days . . .

On that same note, with regard to the Site Wiring Fault, Yikes!  I'll have electrical come check out the room wiring ASAP.

Also, I do like to stay up to date w/ firmware and software issues.  Here is what it tells me:

UPS 05.0

COM 02.1

UBL 05.0

CBL 5.21

Thanks, again!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

OK, silly question. Can you verify the SKU from the front LCD under About? I am struggling by going with "Smart UPS 2200" and the current firmwares. I am guessing it is SMT2200 or SMT2200RM2U and I just want to get you the correct update but I do believe there will be one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

Sorry, I got buried in other things for a bit.  I found SMT2200 under "UPS Part No:" in the "About" menu.  I don't see "SKU" anywhere.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:37 PM . Last Modified: ‎2024-03-21 12:44 AM

No problem - same thing. Per How do I update the firmware of my SMT, SMX, or SMC series Smart-UPS? | FAQs | Schneider Electric US , I believe the latest update is UPS 07.1

That article also outlines the way to update the file via our UPS Firmware Upgrade Wizard and if you ended up getting a network management card, you could push it that way too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of