just bought a BX1500G UPS, few questions

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • just bought a BX1500G UPS, few questions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:34 AM

0 Likes
13
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:34 AM

just bought a BX1500G UPS, few questions

Hi, I've just bought my first UPS, and i have a few questions that I'm not sure of.

here is my situation:

I have a generator that runs my whole house, but when the power goes out, it doesn't come on for about 10-15 seconds, then it kicks in and the power comes back on in the house.

so i bought this unit so i can hook my computers/server to it so its not interrupted while the generator is kicking on, and again when it goes off and the regular power comes back on.

when i say server, its just my older desktop, not a huge big server or anything.

my questions-

can i hook another surge protector into this UPS (NOT into the battery backup outlets), for things such as my TV, monitors, laptop charger, home theater etc (things that arent going to be running 24/7)

the things i need to be on the UPS/battery backup part is my 2 desktop PCs (one is a performance pc with 7 hard drives in it etc)

also, im confused by the "master" outlet on the back, and the ones that say "controlled by master"

any help would be appreciated! i have my stuff all disconnected and wired everywhere right now, re organizing it all nice and neat πŸ™‚

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:26 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:26 AM . Last Modified: β€Ž2024-03-22 02:33 AM

Hi everyone, just a quick question instead of starting another thread. Is this a dead silent ups? It's going to be in my bedroom so I want it to be as quiet as possible.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

Yes, It is a UPS(Uninterrupted Power Supply).

Please refer the UPS user manual for more information on how to install this product. Let us know if you have any further question.

:)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

thanks!

:)

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

Hi VJ,

APC does not recommend to plug a Surge Protector into the output of any Back UPS. Click here for more information. I would recommend you to plug the Surge Protector to the wall directly as any APC Surge Protector can provide protection against harmful surges if it is connected to the outlet which is properly grounded.

"Master" and "Master Controlled Outlets" can be used to conserve energy when the Computer is not is use. It will definitely save some electricity bill πŸ™‚

From the User Manual:

Power-Saving Master and Controlled outlets:
To conserve electricity, configure the Back-UPS to recognize a Master device, such as a desktop computer or an A/V receiver, and Controlled peripheral devices, such as a printer, speakers, or a scanner.
When the Master device goes into Sleep or Standby mode, or turns OFF, the Controlled device(s) will shut down as well, saving electricity.

Enable the Power-Saving feature:
Press and hold MUTE and DISPLAY simultaneously for two seconds. The unit will beep to indicate that the feature is enabled. The leaf icon on the display will illuminate.
Disable the Power-Saving feature:
Press and hold MUTE and DISPLAY simultaneously for two seconds. The unit will beep to indicate that the feature is disabled. The leaf icon on the display will darken.
Setting the threshold:
The amount of power used by a device in Sleep or Standby mode varies between devices. It may be necessary to adjust the threshold at which the Master outlet signals the Controlled outlets to shut down.
1.Ensure a master device is connected to the Master outlet. Put that device into Sleep or Standby mode, or turn it OFF.
2.Press DISPLAY and MUTE simultaneously and hold for six seconds, until the leaf icon flashes three times and the unit beeps three times.
3.The Back-UPS unit will now recognize the threshold level of the Master device and save it as the new threshold setting.

I hope that this helps. Let us know if you have any question.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

Hi, I've just bought my first UPS, and i have a few questions that I'm not sure of.

here is my situation:

I have a generator that runs my whole house, but when the power goes out, it doesn't come on for about 10-15 seconds, then it kicks in and the power comes back on in the house.

so i bought this unit so i can hook my computers/server to it so its not interrupted while the generator is kicking on, and again when it goes off and the regular power comes back on.

when i say server, its just my older desktop, not a huge big server or anything.

my questions-

can i hook another surge protector into this UPS (NOT into the battery backup outlets), for things such as my TV, monitors, laptop charger, home theater etc (things that arent going to be running 24/7)

the things i need to be on the UPS/battery backup part is my 2 desktop PCs (one is a performance pc with 7 hard drives in it etc)

also, im confused by the "master" outlet on the back, and the ones that say "controlled by master"

any help would be appreciated! i have my stuff all disconnected and wired everywhere right now, re organizing it all nice and neat πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

The PC is custom built (I built it myself). I installed a Zallman fan controller that has a wattage meter. When in sleep mode, the power consumption runs about 135 to 138 watts. I'm not sure what you mean about what LEDs are lit when programming the threshold. I simply press the two buttons until the unit beeps three times. It would be nice if you could set the threshold to a specific value from the software but I have not seen this option.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

Hi,

I just bought the same unit at Best Buy. I have set the threshold according to the instructions. I have the PC connected to the master outlet and my monitor and speakers to the accessories outlet. The monitor and speakers do not shut off when the computer goes into sleep mode, only when I shut off the computer completely. I have tried setting the threshold with the computer in sleep mode and the monitor in sleep mode, with the monitor not in sleep mode and with the monitor in sleep mode and the speakers on and with the speakers off but no matter how I set the threshold, I still cannot get the desired effect. I never turn the computer off because I have a windows home server that performs backups overnight. (It is capable of waking the computer for backups.) I want the monitor and speakers to shut off and conserve power when the PC goes to sleep but I can't seem to make this work.
Any help would be greatly appreciated.

Thanks in advance,
Peter Gil

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

For your computer model, do you have any idea of what the normal wattage draw is, and what the draw when in "Sleep" mode changes to? Also can you verify the LEDs that show on the unit when you are in the threshold programming mode and have set the threshold to the lowest value? If you use a different load such as a 100w lamp or other device with a decent wattage rating, and then turn that off, does that successfully turn off the "Controlled by Master" outlets?

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

petergil@verizon.net wrote:The PC is custom built (I built it myself). I installed a Zallman fan controller that has a wattage meter. When in sleep mode, the power consumption runs about 135 to 138 watts. I'm not sure what you mean about what LEDs are lit when programming the threshold. I simply press the two buttons until the unit beeps three times. It would be nice if you could set the threshold to a specific value from the software but I have not seen this option.
I was referring to the leaf icon flashing and the beeping you mentioned. If it was not doing that, that would be troubling. Do you know what the draw on your computer is when it is not in sleep? Also, as I mentioned before does a more static on/off load like a lamp work with the master/controlled functionality?

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:25 AM . Last Modified: β€Ž2024-03-22 02:33 AM

95prelude wrote:Hi everyone, just a quick question instead of starting another thread. Is this a dead silent ups? It's going to be in my bedroom so I want it to be as quiet as possible.
The UPS is not 100% silent, as there is a small fan in it that is needed to cool the unit when it has a high load on it or under certain battery charging conditions. From what I've heard when sitting near these units, I would not find them disrupting in a bedroom but that is personal opinion.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:26 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:26 AM . Last Modified: β€Ž2024-03-22 02:33 AM

I have not tried a lamp but if I turn the PC off completely, then it does shut off the accessories. This is why I think the issue is where the threshold is set. My PC's draw when running is about 164 watts and about 138 when in sleep mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-29 02:26 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:26 AM . Last Modified: β€Ž2024-03-22 02:33 AM

Hi, do you still need assistance with this issue? From your last post it was unclear as to whether or not you had solved the issue on your own. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:26 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:26 AM . Last Modified: β€Ž2024-03-22 02:33 AM

Erasmus,

Thanks for checking back. No, I have not resolved this issue. I am certain I am setting the threshold correctly but the unit will not turn power off to my accessories unless I turn the computer off completely. I really need this feature because for some reason my LCD monitor is not staying in sleep mode and I don't want the lamp to wear out from use. My monitor goes to sleep when the computer goes to sleep but if I come back later, the lamp is on even though the screen is blank and my computer is asleep. I'm afraid this will drain the life from the lamp and would really like for the UPS to cut the power off. Also, the on/off switch on my speakers is on the underside of the subwoofer and very difficult to shut off. I would like this to shut off as well. Right now, I have only the monitor and speakers plugged into the the accessories outlets. Once again, if I shut the computer off, the monitor and speakers shut off but this is not how this feature is advertised. They are supposed to shut off when the computer goes to sleep. Any help would be greatly appreciated!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:26 AM . Last Modified: β€Ž2024-03-22 02:33 AM

0 Likes
0
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:26 AM . Last Modified: β€Ž2024-03-22 02:33 AM

Hi everyone, just a quick question instead of starting another thread. Is this a dead silent ups? It's going to be in my bedroom so I want it to be as quiet as possible.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore