Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

generators, clean power, "true" U.P.S. vs "Back-UPS"

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: generators, clean power, "true" U.P.S. vs "Back-UPS"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:51 PM . Last Modified: ‎2024-03-26 03:12 AM

0 Likes
2
5581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:51 PM . Last Modified: ‎2024-03-26 03:12 AM

generators, clean power, "true" U.P.S. vs "Back-UPS"

We've been on generator power for a couple days (NJ, Isaias).  All the electronics were initially unplugged because early on the power cycled a few times.  I have used a gaming computer and charged a laptop a few times.

Anyway, today I wanted to get something off a home NAS protected by a BR1000G ("Pro 1000"), so I turned them on.  The NAS shut down after a bit.  The "UPS" sees 115v but isn't charging the battery and the battery ran out. According to the troubleshooting chart for the "UPS"...

The AC input voltage is out of range, the frequency is out of range, or the waveform is distorted

That sounds right.  Generators are known to have dirty power and it's a cheap generator.  On one hand I think "nice, it's protecting my NAS from dirty power."  On the other hand

  1. It can't even charge its own battery with dirty power?
  2. Isn't it supposed to clean the power?

I unplugged all loads and adjusted the sensitivity and it still wont charge.  Then I do some searching and find an article describing the difference between "true" "Uninterruptible power supplies" and "battery backups".

According to the article, only the former provide clean power when the input power is on and some battery backup products are labeled "UPS" by some manufacturers even though they're not true UPSs.  Sure enough, checking the manual for my "Back-UPS" product, I don't see "uninterruptible" used anywhere.

Is this correct?  I have a "battery backup" product that is not a true UPS despite having "UPS" written all over it?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • br1000g
  • generator
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-06-28 05:51 PM . Last Modified: ‎2024-03-26 03:11 AM

0 Likes
0
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:51 PM . Last Modified: ‎2024-03-26 03:11 AM

The terms UPS and Battery backup arent really set in stone.  They dont have any clear definitions.   

APC used to distinguish between their Backups v. Smartups lines to imply the type of power conditioning/protection that they offer.   But even that has merged because AVR technology is so cheap.

So now all APC units are power protection devices... protect against bad power and no power.

The cheapest way to protect power now is to use the batteries to condition the power and replace the power during an outage.   This means the batteries become depleted if it has to do this power conditioning continuously.

The other UPS alluded to by the other response was an Online UPS.   This type of UPS will say "Online".. like Smart Online in the name.  In these units, the UPS takes any sort of trashy power, converts it to DC, the rebuilds it to AC.  This Double conversion works great for generators as it does not care what power or frequency you give it, it will still keep the batts charged and create perfect power out.  APC models starting with SURT and SRT are your online units.  Liebert's line uses GXT to signal online.   Tripplite... SU

BTW - check you generator's frequency.  Often its the frequency that is off, more so than the AC voltage.

 

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:51 PM . Last Modified: ‎2024-03-26 03:11 AM

0 Likes
0
5578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:51 PM . Last Modified: ‎2024-03-26 03:11 AM

Hi Troy,

I'll give you a short answer that's close enough and a really long answer, there is more than two types of UPS but we'll focus on three:

Standby - Battery kicks in when power is off or unacceptable, output inventor is off 

Line interactive - Battery kicks in when power is off or unacceptable but also does a higher level of cleaning, (particularly around voltage not really around the wave) and is faster to react, the output inventor is always on.

Double conversion or "Online" - All power is cleaned and outputted as a sin wave approximation, "dirty" power comes in, it's converted to DC which with the battery powers the output inverter which converts it back to AC, this is what we recommend for generators but it is almost our most expensive. (There is also delta wave conversion but I'm not an electrical engineer so we'll leave that alone)

The long answer is to have a look at this white-paper, like I said I'm not an electrical engineer but I understood most of it so you might be okay, Obvious I work with a lot of UPSs so that probably helped me understand.

  https://download.schneider-electric.com/files?p_Doc_Ref=SPD_SADE-5TNM3Y_EN

Reply

Link copied. Please paste this link to share this article on your social media post.

chefash_apc
Ensign chefash_apc
Ensign

Posted: ‎2021-06-28 05:51 PM . Last Modified: ‎2024-03-26 03:11 AM

0 Likes
0
5579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:51 PM . Last Modified: ‎2024-03-26 03:11 AM

The terms UPS and Battery backup arent really set in stone.  They dont have any clear definitions.   

APC used to distinguish between their Backups v. Smartups lines to imply the type of power conditioning/protection that they offer.   But even that has merged because AVR technology is so cheap.

So now all APC units are power protection devices... protect against bad power and no power.

The cheapest way to protect power now is to use the batteries to condition the power and replace the power during an outage.   This means the batteries become depleted if it has to do this power conditioning continuously.

The other UPS alluded to by the other response was an Online UPS.   This type of UPS will say "Online".. like Smart Online in the name.  In these units, the UPS takes any sort of trashy power, converts it to DC, the rebuilds it to AC.  This Double conversion works great for generators as it does not care what power or frequency you give it, it will still keep the batts charged and create perfect power out.  APC models starting with SURT and SRT are your online units.  Liebert's line uses GXT to signal online.   Tripplite... SU

BTW - check you generator's frequency.  Often its the frequency that is off, more so than the AC voltage.

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore