New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
constant Red light and beeping issue with APC 1100bx
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-2907:55 PM
constant Red light and beeping issue with APC 1100bx
so, when I turn off my Pc I still leave my ups on, but whenever I turn off the UPS after its plugged in and not used for a long time (say 4-5 hrs), the red-light blinks and it constantly beeps. It only goes off when I plug it in again. It doesn't make any issue when Plug out the ups immediately after turning off the PC.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-2106:01 AM
Hi Chanu,
Perhaps you have already found the answer. But for completeness sake, I will try to answer your question.
Can you advise when you turned off the UPS, is the UPS plug pulled out or connected to AC mains but the power is off?
If yes, then the UPS will think that there is no power to equipment and switch to Battery mode. It will slowly discharge until low battery and LED will blinks and constantly beep. This is normal as all UPS are designed this way. It is not supposed to be off.
You can turn off the UPS to completely turn off the connected equipment. But the UPS should be always plugged in to a mains plug (in ON position) so it will trickle charge.
The only way to stop the UPS completely is to pull out the Battery Connector to disconnect the acid batteries. But then, it is troublesome and it is not really the purpose of the UPS.
I have same question in my head once, and got the answer after some research.