bn1500m2 wont pass self test

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • bn1500m2 wont pass self test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

0 Likes
8
2302
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

bn1500m2 wont pass self test

Hi

I purchased the Back-UPS Pro 1500VA Battery Back-Up System Model : BN1500M2 less then a year ago in April as a matter of fact from Best Buy and it just attempted to perform it's weekly self test and for some reason failed it and started screeching I reseeded the battery tried rebooting  turned the unit off  and back on it continued screeching I then turned it off and back on again and then it came on normally

I went to try and do another self test .. it failed and started screeching I rebooted still screeching  rebooted again it booted fine

At this point I'm afraid to try a self test

Since this unit is less then a year old Anyone have any ideas or suggestions

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

0 Likes
0
2304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

You certainly can store the batteries in a closet so long as it does not become excessively hot or cold in there.

If the batteries are to be stored for more than six months, they should be charged every six months or so.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

0 Likes
0
2304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

Hi Chad,

Can you please try to braindead the UPS. To do this please follow the steps below:

1: Disconnect any attached load.

2: Unplug the UPS from the wall socket.

3: Disconnect the UPS' internal battery.

4: Push and hold the ""On"" button on the UPS for 5 seconds

5: Reconnect internal battery.

6: Plug UPS in to known good power source.

7: Turn UPS on.

Can you also provide the serial number of the UPS?

Regards,

Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

0 Likes
0
2304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

Will try.

Thanks

The serial number you asked for 3B1743X09436 

Should I try running a self test after those steps?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

0 Likes
0
2304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

I just tried your suggestion then I ran a self test and... it passed I don't know why it passed  Seriously I'm curious  why did that work?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

0 Likes
0
2304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

Well disregard the last post it just failed the self test

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

0 Likes
0
2305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

Ok Well apparently since it passed the self test after your suggestion Thomas then failed again 20 mins later that would make the problem intermittent I had to go to Best Buy on Thanksgiving and get a new one.. I must have a death wish going there today..

I will be contacting APC Customer service about a replacement since the unit has a 3yr warranty and it only lasted 7 months

Hope they are open on Black Friday

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

0 Likes
0
2305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

Hi Chad,

Very sorry this disrupted your Thanksgiving. Yes our customer service is open today. They can be contacted at 800-555-2725.

Regards,

Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

0 Likes
0
2305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

I have received new batteries for my previous unit  

Is there a proper way to store these batteries till  I get them installed or is it okay to put them in the closet?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

0 Likes
0
2305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:36 AM . Last Modified: ‎2024-03-26 04:09 AM

You certainly can store the batteries in a closet so long as it does not become excessively hot or cold in there.

If the batteries are to be stored for more than six months, they should be charged every six months or so.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore