back ups 1400 auto turn off

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • back ups 1400 auto turn off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-26 10:42 PM

0 Likes
1
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-26 10:42 PM

back ups 1400 auto turn off

I have a new back ups 1400 , I use it for my labtop and Internet router , I connected the ups with usb cable to my labtop to turn off the alarm every 30 sec , but every 8 min ups turn off and power shute program make my computer to turn off , this period can not be increse from power shute program , and if i did not connect the ups with the usb cable, this problem is solved but the alarm sound is annoying . i need to turn off alarm as the same time the ups dont turn off every 8 min and i have to turn it on again 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-26 10:42 PM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-26 10:42 PM

Hi Youssef,

UPS can able to shutdown the computer only if the UPS is operating on battery mode. Based on the information which you have provided looks like the UPS is switching to on battery (voltage fluctuation or power outage) and after 8 mins it is turning off the computer because of the shutdown configured on the PCPE software. If you just looking to disable the alarm then you can choose the option in the PCPE software to disable the audible alarm and then you can disconnect the cable from UPS. Also, I would try setting the voltage sensitivity to low from the software before unplugging the cable. Let me know if this helps you?

Regards,

Vinay

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-26 10:42 PM

0 Likes
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-26 10:42 PM

Hi Youssef,

UPS can able to shutdown the computer only if the UPS is operating on battery mode. Based on the information which you have provided looks like the UPS is switching to on battery (voltage fluctuation or power outage) and after 8 mins it is turning off the computer because of the shutdown configured on the PCPE software. If you just looking to disable the alarm then you can choose the option in the PCPE software to disable the audible alarm and then you can disconnect the cable from UPS. Also, I would try setting the voltage sensitivity to low from the software before unplugging the cable. Let me know if this helps you?

Regards,

Vinay

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore