XS 1500 Battery Test Failing Half Of The Time When The Batteries Appear Fine

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • XS 1500 Battery Test Failing Half Of The Time When The Batteries Appear Fine
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:45 AM . Last Modified: ‎2024-03-26 04:01 AM

0 Likes
4
795
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:45 AM . Last Modified: ‎2024-03-26 04:01 AM

XS 1500 Battery Test Failing Half Of The Time When The Batteries Appear Fine

I started getting a battery test failed message on my UPS, it was probably 4 years old, i could run the test again and it would sometimes say it is just fine. I went ahead and bit the bullet, bout replacement batteries for it, it immediately failed the test when it said the batteries had 100% charge, so i let it run down to like 5 minutes left out of 30-45, let it charge back up, re-ran test, test ok, marked battery as changed in APC software. Just now I had a message it failed again, ran test, failed again, waited a minute ran test, passed.

I have checked the batteries and both are strong, the wiring connecting the 2 is all in perfect condition, the pins on the receptacle to connect to up look very good.

Anyone else have this issue?

I could not fine the exact slide in insert so i got two identical batteries, and rebuilt the pack, i doubt this has anything to do with it as this failure issue was happening with the original batteries. i have good power here, UPS does not have to intervene much at all.

Disconnected Main, UPS ran on battery just fine for awhile, was beeping about a bad battery but was giving me very accurate time left readings, after letting it run on the battery for 5 or 10 minutes. it has 4 out of 5 charge, and all tests are now showing good, i already cycled these new batteries when installed like a month ago.

The UPS does not appear to be crapped out as it is functional, it has no problem running on battery and keeping things up and going fine, even for the long haul, i wonder if my original batteries were not still good, or still ok at least, seems to be something in the testing process. not sure why its failing?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:46 AM . Last Modified: ‎2024-03-26 04:01 AM

0 Likes
0
795
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:46 AM . Last Modified: ‎2024-03-26 04:01 AM

I’ll give that a shot, however the software is correctly triggering the ups to perform internal test and the bad indicator is showing up on the ups itself

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:45 AM . Last Modified: ‎2024-03-26 04:01 AM

0 Likes
0
795
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:45 AM . Last Modified: ‎2024-03-26 04:01 AM

Hi Ash,

It is important to run the self-test with your typical configuration powered on during the test. Changing the battery replacement date (which you appear to have done) in the PowerChute software should help to adjust the battery constants of the UPS to identify the new battery. If your original batteries were 4yrs old, it's safe to say the likely required replacement. Typical battery life is between 3-5yrs depending upon the environment in which they are installed. How much load do you have applied during your tests? How much runtime remaining is showing on the UPS vs the Powerchute Software?

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:45 AM . Last Modified: ‎2024-03-26 04:01 AM

0 Likes
0
795
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:45 AM . Last Modified: ‎2024-03-26 04:01 AM

Load is around 19% or 1 bar, both software and ups show around 35 minutes runtime, wattage ranges from 150 to 250. I have tested the ups twice once right after replacement and failure message used a 200 watt work light and it performed as expected. Ran another test and it kept everything normal up for 10 minutes and was time decreasing properly and drained the battery by 1 bar which then let all tests results show up good again.

by all performance tests I have done I see nothing wrong, It just complains on tests sometimes. The batteries both measured and right over 12 so no dead cells on my replacements

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:45 AM . Last Modified: ‎2024-03-26 04:01 AM

0 Likes
0
795
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:45 AM . Last Modified: ‎2024-03-26 04:01 AM

I would agree, it sounds as if the UPS is operating as expected. I might recommend you un-install the version of PowerChute you have installed and try and install the latest version. 

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:46 AM . Last Modified: ‎2024-03-26 04:01 AM

0 Likes
0
796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:46 AM . Last Modified: ‎2024-03-26 04:01 AM

I’ll give that a shot, however the software is correctly triggering the ups to perform internal test and the bad indicator is showing up on the ups itself

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of