Works when plugged it but not on battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Works when plugged it but not on battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

0 Likes
6
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

Works when plugged it but not on battery

Over the last few hours I've been searching the forum and although people seem to have similar problems, they don't have the exact one I'm having.

I've currently got a sump pump plugged in to my Smart-UPS 1400. If my calculations are correct, the 5.7 amp pump should use about 684 watts. Which should be no problem for the 950w max that the 1400 supports.

When the unit is plugged in and the pump starts, the overload flashes for a brief 1/10th of a second, and then turns off after the pump starts (while running the 2/5 lights are lit up). However, when the unit is not plugged in and running on batteries, the pump is never able to get past it's startup and stalls.

I started with a Smart-UPS 1000 which peaks at 670(ish) watts, so I went out an bought a 1400 thinking I was maxing out the wattage.

Is the 1400 overloaded too or do I have a battery issue or a configuration issue?

Thanks for any input you guys can offer

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:49 AM . Last Modified: ‎2024-03-22 03:53 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:49 AM . Last Modified: ‎2024-03-22 03:53 AM

how many load LEDs are present on the left hand side of the UPS while the UPS is online and then while on battery?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

Hi:

It sounds like the inrush current of your sump pump may be a bit too much for this UPS to handle. While your current calculations for this do sound correct, that is likely the current draw while the pump is operating. The draw when it is first powering up is likely much higher. You might try contacting the pump manufacturer about what the max inrush current is when the pump starts up, then size the UPS that way. Let us know if we can be of more assistance!

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

Thank you for your speedy and informative response. I will try to contact the pump company or do some research to find out the initial draw.


If I am exceeding the UPS's limit, why would it supply power just fine when it's plugged in but not when it's on battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

From what I've tried to find, it does look like I'm exceeding the UPS's limit.

But, if I am exceeding the UPS's limit, why would it work when plugged in but not on battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

When the pump starts (on batteries or plugged in), the overload light quickly blinks, then all 5 lights are on.

When the UPS is plugged in, the pump starts. When the UPS is on batteries the pump tries to start, then doesn't get over it's initial starting phase and doesn't start pumping the water. If I monitor the 110v plug on the back of the UPS, it dips way down around 40v... (according to the pump manufacturer, it doesn't start properly unless the voltage is above 108v).

Thank you for your response.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:48 AM . Last Modified: ‎2024-03-22 03:53 AM

hmm ok. so as the amperage draw goes up, the voltage should go down, which seems to be what we are seeing here.

so while that voltage draw is 40v, are all 5 load LEDs still on even though the pump hasnt fully started?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:49 AM . Last Modified: ‎2024-03-22 03:53 AM

0 Likes
0
1171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:49 AM . Last Modified: ‎2024-03-22 03:53 AM

how many load LEDs are present on the left hand side of the UPS while the UPS is online and then while on battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore