Why do we need online UPS configuration

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Why do we need online UPS configuration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:47 AM

0 Likes
5
1758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:47 AM

Why do we need online UPS configuration

Hey Forum
I have been out of the game a for while and have been brought in to look at a troublesome critical electrical supply circuit.

Firstly though I am curious about why we need to configure a UPS in online mode, I have been told these are using the UPS power all the time instead of coming up when the mains fails (i.e. standby mode).

Back in the day I had my server room AS400s hooked up to a UPS which was in standby mode, I never had issues with a power up delay causing the AS400s to suffer from brown outs. Believe me this UPS would have to click on and operate 20 times a day at least. It took a lot of detective work and we found that the sari shop downstairs (on the same electrical feeder) had a big Daikin AC unit that would drop the voltage and click on our UPS every time the compressor ran. I loved those days in Sri Lanka.

So whats wrong with UPS in standby mode? Is it just a fad because the technology is now cheaper? I need to know because I may need to suggest a UPS in standby mode to satisfy the issue we have with this system.

TIA

Multivits

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

0 Likes
0
1758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

Hey Forum
I have been out of the game a for while and have been brought in to look at a troublesome critical electrical supply circuit.

Firstly though I am curious about why we need to configure a UPS in online mode, I have been told these are using the UPS power all the time instead of coming up when the mains fails (i.e. standby mode).

Back in the day I had my server room AS400s hooked up to a UPS which was in standby mode, I never had issues with a power up delay causing the AS400s to suffer from brown outs. Believe me this UPS would have to click on and operate 20 times a day at least. It took a lot of detective work and we found that the sari shop downstairs (on the same electrical feeder) had a big Daikin AC unit that would drop the voltage and click on our UPS every time the compressor ran. I loved those days in Sri Lanka.

So whats wrong with UPS in standby mode? Is it just a fad because the technology is now cheaper? I need to know because I may need to suggest a UPS in standby mode to satisfy the issue we have with this system.

TIA

Multivits

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

0 Likes
0
1758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

Thanks Voidstar

The issue is that the UPS has failed for a second time. I have the replacement ready to be installed. Our facility in brand new and this particulat circuit was a late add on and we knew virtually nothing about until I had to step in and start by drawing it all out.

The primary need for the circuit is to provide mains power to critical equipment during our transition form mains to our onsite gas fired gen sets. Normally our gen sets run it grid parrallel import mode (because we utilise waste exhaust heat for chilled and hot water services, but that another story).

But if the grid fails we can switch into complete island mode and run from the gen sets. The problem is that we need a source of electrical power to keep the auto gas shut off valves open (or the gens set stop, catch 22), the BMS system up (so that it can control the load shed and the controlled re-powering sequencing of the main DBs around the facility) and to power the motorised contactors (which bring on each main electrical panel).

Firstly we don't know exactly what else is connected to the UPS (I am planning to trace the cabling and draw it and label it). When we know we can calculate actual up time based upon current load.

The UPS feeds through a FG Wilson auto transfer switch, the UPS is connected as the "mains" input. The "gen" input to the transfer switch is a regular feed from an adjacnet panel. When the UPS fails the transfer switch goes to "gen" mode (which is really just mains).

I don't like this set up because to me it is flawed if the online UPS fails (like it now has). I have been trying to figure out a way of putting a second UPS in standby mode on the "gen" input the the transfer switch but it starts getting tricky to cover all scenarios. I have attached the circuit drawingh as we currently know it.

Are there similar appliactions and circuits that we can use or if anyone has a good idea to give us at least one level of redundancy.


TIA
Multivits

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

0 Likes
0
1756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

>
I don't like this set up because to me it is flawed if the online UPS fails (like it now has). I have been trying to figure out a way of putting a second UPS in standby mode on the "gen" input the the transfer switch but it starts getting tricky to cover all scenarios. I have attached the circuit drawingh as we currently know it.
>

I'll bet. The APC solution is to use a redundant UPS like Symmetra. Two advantages of Symmetra over having two separate UPSes:
- Two UPSes means you're buying twice the power, twice the batteries, etc. Symmetra uses an extra power module and extra batteries to get redundancy.
- If the UPS is hardwired, an electrician is needed to replace a failed UPS. Symmetra modules are user-swappable.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

0 Likes
0
1756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

in addition to a modular and redundant UPS, you could also look into a service bypass panel which will give you a wrap around bypass. this means that if you need to take a UPS out of operation for any reason, you can use the wrap around bypass to bypass the UPS without taking your load down.

[here is a user manual for some of the service bypass panels|http://www.apcmedia.com/salestools/SCON-7Q3JQ2_R0_EN.pdf]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

0 Likes
0
1756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

Thanks "Picked a Winner"

Yes there is already a Service Bypass Panel (on the CCT diagram it is included in the UPS box).

We can also take the UPS out of service because of the feed into the transfer switch.

But my real concern is about supporting our essentials during the generators start up and shed if we have a failed UPS. As stated the generators can not start in a blackout situation unless the UPS is up to supply the gas auto shut off valve (and others).

TIA

Multivits

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

0 Likes
0
1759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:08 PM . Last Modified: ‎2024-03-20 05:46 AM

Hey Forum
I have been out of the game a for while and have been brought in to look at a troublesome critical electrical supply circuit.

Firstly though I am curious about why we need to configure a UPS in online mode, I have been told these are using the UPS power all the time instead of coming up when the mains fails (i.e. standby mode).

Back in the day I had my server room AS400s hooked up to a UPS which was in standby mode, I never had issues with a power up delay causing the AS400s to suffer from brown outs. Believe me this UPS would have to click on and operate 20 times a day at least. It took a lot of detective work and we found that the sari shop downstairs (on the same electrical feeder) had a big Daikin AC unit that would drop the voltage and click on our UPS every time the compressor ran. I loved those days in Sri Lanka.

So whats wrong with UPS in standby mode? Is it just a fad because the technology is now cheaper? I need to know because I may need to suggest a UPS in standby mode to satisfy the issue we have with this system.

TIA

Multivits

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore