What UPS to get for an Apple Mac Pro?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • What UPS to get for an Apple Mac Pro?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:08 AM

0 Likes
7
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:08 AM

What UPS to get for an Apple Mac Pro?

I'm in the market for a UPS for my Mac Pro. My box is a 3.0 GHz 6 GB RAM, 4 internal HDDs, 2 Superdrives, XT1900, 7300GT system driving two 22" LCD and one 24" LCD displays. I'm thinking I want something in the 1500AMP range but I want it to be able to shut my Mac down if the UPS is getting low and I absolutely must be able to turn off any audio warning beeps forever.

Any Suggestions? Does APS's Smart UPS 1500 (SUA1500) fit the bill? The no beeping thing is a hot button for me.

Thanks for any help!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

0 Likes
0
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

In order to get the ability to turn off the sound, you will need to install PowerChute Business Edition.

[http://www.apcc.com/tools/download/login.cfm?software_id=DBUE-6TCJWP&sw_sku=SFPCBE705]

The installation for Business Edition can be complicated, but for what you want to do, you won;t need to install the whole thing.

1. Before you start with business Edition, get rid of Personal Edition.
2. Start the installer for Business Edition, choose to install the basic version, and install only the Agent.
3. At some point of the Agent installation, it should attempt (and succeed) to discover your Smart-UPS.
4. Enter a username and password of your choice when prompted.

At this point, you would normally go on to install the other components, but you can use the Agent by itself, through its web interface, to disable the sounds. You can log into the web interface by opening a java enabled web browser, and enter the address of the computer that has the Agent installed on it - specifying port 3052.

For example, your URL should look like this: http://:3052 where would be substituted by the actual IP address of the Windows computer you installed the Agent on. You may even be able to use the computers loopback address by setting the URL to http://127.0.0.1:3052.

Once you get the browser pointed to the correct address, you should be prompted to log into the PowerChute Agent. Use the username and password you specified in the installation. I think the option to turn off the beeping is in the Diagnostic menu, but if its not there, fish around and I'm sure you will find it in one of the menus.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:08 AM

0 Likes
0
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:08 AM

If you're buying or already have a new Mac Pro, do not bother to install any APC software. First of all, the PowerChute software that's available is not fully compatible with the latest iterations of Mac OS X 10.4 Tiger, which you have on your Mac Pro.

Secondly, you're right that just by connecting the USB data cable to your Mac from the UPS, your Energy Saver System Preference will know exactly which APC UPS you have and a little UPS icon will appear near the clock in the top right of your menu bar. Energy Saver will be able to tell you your battery capacity and will allow for UPS specific shutdowns.

Congrats on buying such a great computer and UPS!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:08 AM

0 Likes
0
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:08 AM

Apple says this unit has a maximum draw of 12A, which just happens to be the full amount of current you can safely draw from a single 15A circuit. With your configuration, your inrush current may actually come close to that 12A mark, especially if you have any other peripherals plugged into your UPS.

I would say the minimum UPS would have to be the SUA1500 (yes, you can permanently disable alarms via software). Maybe get a Kill-A-Watt for $25 and just see how many watts you draw when using your Mac Pro, and also when your system boots up from completely off state.

If the specs of the SUA1500 cover you, then you'll be OK with that model. Chances are you leave your Mac Pro on most of the time and it's nominal amp draw is well below the 12A max listed.

You'll no doubt get quite a few suggestions on which UPS to buy, especially if you require significant runtime (which you didn't specify).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

0 Likes
0
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

I'm a little confused by the products APC offers. There are several 1500 APCs offered, will they all try to shut down my Mac if batteries run too low or only the Smart-UPS?

Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

0 Likes
0
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

I ended up going with the Smart-UPS 1500. My understanding is that when I plug in the UPS with a USB cable, the Energy Saver control panel or system preference from within OS X will offer new features to control the UPS. Although impossible to find on APC's web site without somebody posting a link, PowerChute v1.3.4 may allow OSX to fiddle with UPS's settings.

The trouble with all of this is APC's web site is bewildering and difficult to find answers on?and then, conflicting answers are often found. Figuring out what UPS to get shouldn't be hard. The most useful information I found was from this disccussion forum:

APC Discussion Forums : Back-UPS ES 700 and OS X software ...

APC should have a line chart with what products support what platforms that includes links to the products and supporting applications. Why has the obvious escaped marketing? Why did I have to fiddle around trying to learn what product would work with my Mac?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

0 Likes
0
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

The beeping on a Smart-UPS 1500 can be disbaled, but only through software that runs on a Windows based computer. The PowerChute software for Mac doesn't have as many features as the Windows based, and this includes the ability to turn the beeping off. If you were able to load the Business Edition software on a Windows machine just to disable the beeping, that setting would stay with the UPS even after you disconnected it, and moved it to the Mac computer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

0 Likes
0
3019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

Thank you dirtfoot, JoeMomma.

On the Mac OSX side, the Mac immediately recognized the Smart-UPS 1500; but as dirtfoot said, OSX doesn't have the ability to shut off the noise maker. So I fired up on a XP boot drive and downloaded PowerChute 2.0 for XP. On installation, the PowerChute application refused to install because I don't have a supported UPS connected. What do I need to do? I plugged in the UBS cable between my Mac and the Smart-UPS and I checked the "Add Hardware" control panel which has told me that the UPS is connected and functioning. In the Device Manager the Smart-UPS shows up as HID UPS Battery, not as a Smart-UPS. I presume that HID UPS Battery is a generic entry but the end result is that i am unable to install the PoweChute 2.0 for XP software. Is there more to it?

Message was edited by: EricTheOracle

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

0 Likes
0
3020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:43 PM . Last Modified: ‎2024-03-26 02:07 AM

In order to get the ability to turn off the sound, you will need to install PowerChute Business Edition.

[http://www.apcc.com/tools/download/login.cfm?software_id=DBUE-6TCJWP&sw_sku=SFPCBE705]

The installation for Business Edition can be complicated, but for what you want to do, you won;t need to install the whole thing.

1. Before you start with business Edition, get rid of Personal Edition.
2. Start the installer for Business Edition, choose to install the basic version, and install only the Agent.
3. At some point of the Agent installation, it should attempt (and succeed) to discover your Smart-UPS.
4. Enter a username and password of your choice when prompted.

At this point, you would normally go on to install the other components, but you can use the Agent by itself, through its web interface, to disable the sounds. You can log into the web interface by opening a java enabled web browser, and enter the address of the computer that has the Agent installed on it - specifying port 3052.

For example, your URL should look like this: http://:3052 where would be substituted by the actual IP address of the Windows computer you installed the Agent on. You may even be able to use the computers loopback address by setting the URL to http://127.0.0.1:3052.

Once you get the browser pointed to the correct address, you should be prompted to log into the PowerChute Agent. Use the username and password you specified in the installation. I think the option to turn off the beeping is in the Diagnostic menu, but if its not there, fish around and I'm sure you will find it in one of the menus.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore