Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

What UPS is the right one?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • What UPS is the right one?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:30 PM . Last Modified: ‎2024-03-26 12:25 AM

0 Likes
2
1148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:30 PM . Last Modified: ‎2024-03-26 12:25 AM

What UPS is the right one?

I bought a BX1300LCD. I'm connecting my computer, LCD monitor, external HD, modem, router, speakers and a laser printer to the UPS. I have following questions:
1- I want to know if I have bought the right one, or maybe I can get one with less power. Mt laser printer when connected to the Back-up draws a lot of wattage (the wattage indicator goes over 800W) and the device start beeping, so I connected the printer to the surge only.
2- Does AVR protect only from extremely low voltage like 90 V (as the manual says) or it protects from high voltage, as well.
3- Somebody was complaining about the noisy fan in this device in his review. Does it have a fan? I don't hear anything.

P.S. My last surge protector without APR (from other company) started beeping every time I printed, even though printer was connected to surge only plug-in. I called them, they said it's because I don't have AVR. I think it’s nonsense. What do you think?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:31 PM . Last Modified: ‎2024-03-26 12:25 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:31 PM . Last Modified: ‎2024-03-26 12:25 AM

karte wrote:
I bought a BX1300LCD. I'm connecting my computer, LCD monitor, external HD, modem, router, speakers and a laser printer to the UPS. I have following questions:
1- I want to know if I have bought the right one, or maybe I can get one with less power. Mt laser printer when connected to the Back-up draws a lot of wattage (the wattage indicator goes over 800W) and the device start beeping, so I connected the printer to the surge only.
2- Does AVR protect only from extremely low voltage like 90 V (as the manual says) or it protects from high voltage, as well.
3- Somebody was complaining about the noisy fan in this device in his review. Does it have a fan? I don't hear anything.

P.S. My last surge protector without APR (from other company) started beeping every time I printed, even though printer was connected to surge only plug-in. I called them, they said it's because I don't have AVR. I think it’s nonsense. What do you think?
#1: Do you must have the printer usable during an outage? If so, get a really big UPS capable of supporting it or get an inkjet printer that uses far less power.

The tech support jockey you talked to had no idea what they were talking about. Laser printers pull current abruptly and causes a voltage dip, much like how lights dim when you turn on a vacuum. Some UPSs will see this as an abnormality and complain. This depends on the sensitivity which may or may not be adjustable.

The best solution is to put the laser printer on a branch circuit that is not shared by anything sensitive to voltage sags.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 09:30 PM . Last Modified: ‎2024-03-26 12:25 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:30 PM . Last Modified: ‎2024-03-26 12:25 AM

Hi,

First off, I'd like to note that APC recommends that a laser printer shouldnt be plugged into the battery back up side. When a laser printer warms up it can draw up to maybe around 1000 watts or more and definitely overload the smaller UPSs. If its a smaller Back UPS, it could also do that while plugged into the surge protection side. It just draws so much power and overloads the entire UPS/surge protector unit. If you do need to plug it in, you might want to get the laser printer its own surge protector on its own outlet or circuit.

The easiest way to see if this is the "right" unit would be to see how much wattage (without the laser printer) the UPS is drawing which the UPS should be able to tell you now via the LCD or Powerchute software. So, what is the unit reporting without the laser printer in the picture? If its like 300 watts then you might be able to look at something smaller, such as a BR900 for instance which tops out at 540 watts. But we also need to have a bit of overhead maybe when you are doing some heavy processing or using all of your items at once. It also depends on how much runtime you want.

The unit does have a fan.

And to answer your last question about no AVR causing an overload on a surge outlet, I'd like to hear the reasoning. AVR adjusts your voltage if its too high or too low coming in to the UPS so I am not sure how that could make a difference..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:31 PM . Last Modified: ‎2024-03-26 12:25 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:31 PM . Last Modified: ‎2024-03-26 12:25 AM

karte wrote:
I bought a BX1300LCD. I'm connecting my computer, LCD monitor, external HD, modem, router, speakers and a laser printer to the UPS. I have following questions:
1- I want to know if I have bought the right one, or maybe I can get one with less power. Mt laser printer when connected to the Back-up draws a lot of wattage (the wattage indicator goes over 800W) and the device start beeping, so I connected the printer to the surge only.
2- Does AVR protect only from extremely low voltage like 90 V (as the manual says) or it protects from high voltage, as well.
3- Somebody was complaining about the noisy fan in this device in his review. Does it have a fan? I don't hear anything.

P.S. My last surge protector without APR (from other company) started beeping every time I printed, even though printer was connected to surge only plug-in. I called them, they said it's because I don't have AVR. I think it’s nonsense. What do you think?
#1: Do you must have the printer usable during an outage? If so, get a really big UPS capable of supporting it or get an inkjet printer that uses far less power.

The tech support jockey you talked to had no idea what they were talking about. Laser printers pull current abruptly and causes a voltage dip, much like how lights dim when you turn on a vacuum. Some UPSs will see this as an abnormality and complain. This depends on the sensitivity which may or may not be adjustable.

The best solution is to put the laser printer on a branch circuit that is not shared by anything sensitive to voltage sags.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.