Water pump UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Water pump UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
ac_apc
Crewman ac_apc
Crewman

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

0 Likes
4
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

Water pump UPS

Hi,

We have a water pump (sump pump) that requires to stay on for as long as possible, in case of power failure. The pump is activated/deactivated automatically according to (heavy) rain-water flow. The pump is rated at 11.5 Amps, 115V, 1 phase.

Power regulation and surge suppression should not be issues but pump continuity during powerstorms is crucial. We are in a major city where power grid is good.

What battery back-up/ups should we get?

Thank you.
Cheers,
ac

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • battery
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ac_apc
Crewman ac_apc
Crewman

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

0 Likes
0
2116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

Hi,

We have a water pump (sump pump) that requires to stay on for as long as possible, in case of power failure. The pump is activated/deactivated automatically according to (heavy) rain-water flow. The pump is rated at 11.5 Amps, 115V, 1 phase.

Power regulation and surge suppression should not be issues but pump continuity during powerstorms is crucial. We are in a major city where power grid is good.

What battery back-up/ups should we get?

Thank you.
Cheers,
ac

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

0 Likes
0
2115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

I very seriously doubt that a 1500VA UPS will be able to handle the startup current of the pump, which is typically 6 times the normal running current.

On top of that APC dont list the output waveform type so I doubt its true sinewave (like SUA) which you would want for a motor.

Your best bet is to find out the startup current of the pump (under load, not dry) multiply that by your voltage (115) then devide by 0.6, that will give you the approximate VA needed then I would be inclined to add another 30-40% headroom just to make sure.

On top of that you should really have a true sinewave output when the UPS is on batteries so you're not looking at a cheap setup.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

0 Likes
0
2116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

I'd buy something like this. Its designed for exactly what you want. The reviews for this particular model aren't good but I'm sure there are some units out there that may be better.

http://www.amazon.com/Simer-A5000-Hole-Battery-System/dp/B000DZKXC2

Message was edited by: upsguy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

0 Likes
0
2115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

i agree you may need a larger UPS such as a 2200 VA model to handle the start up current. FYI, everything EXCEPT Back UPS, J type AV units, and Smart UPS SC output a pure sinewave. the Back UPS/Smart UPS beginning with BE, BX, BR, BP, BN, J type AV models, and SC all output a step approximated sinewave which will not work well with a motor load.

Reply

Link copied. Please paste this link to share this article on your social media post.

ac_apc
Crewman ac_apc
Crewman

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

0 Likes
0
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:11 PM . Last Modified: ‎2024-03-20 05:43 AM

Hi,

We have a water pump (sump pump) that requires to stay on for as long as possible, in case of power failure. The pump is activated/deactivated automatically according to (heavy) rain-water flow. The pump is rated at 11.5 Amps, 115V, 1 phase.

Power regulation and surge suppression should not be issues but pump continuity during powerstorms is crucial. We are in a major city where power grid is good.

What battery back-up/ups should we get?

Thank you.
Cheers,
ac

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore