Voltage while on battery is only 93v,is that normal?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Voltage while on battery is only 93v,is that normal?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:03 PM . Last Modified: β€Ž2024-03-22 04:26 AM

0 Likes
8
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:03 PM . Last Modified: β€Ž2024-03-22 04:26 AM

Voltage while on battery is only 93v,is that normal?

The UPS is a BR1500.I have a true RMS multimeter that I used to measure that.I have also the BR24BP attached to the UPS,and this voltage was measured while both external and internal batteries were full and I unplugged it out of the outlet just to test that.Isn't that too low?All the equipaments I have attached to it works with no apparent problem,but I'm afraid that this might be an issue for some types of products that I could need to use on the UPS in the future.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

How was this problem discovered? Did the UPS previously work properly? You say that all your equipment works properly. It is HIGHLY likely that your "true-RMS" multimeter is in fact, NOT True-RMS. This is very likely given that the reading between your two multimeters are very similar, which would make perfect sense given they are both NON-true RMS.

So are simple devices, such as an incandescent light bulb, not working properly while the UPS is operating on-battery? Of course, a light bulb will go very dim when the UPS goes on-battery if what you are saying is true about the voltage dropping to near 90vAC. No multimeter needed to perform this conclusive test.

I think this would perhaps be the best, if not most simple test you can try.

Does the UPS report through software that is is providing 90v, or does it indicate normal 115v battery output?

I believe there to be no problem, other than the way your multimeter was marketed as being true-RMS -- which is very likely is not.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:03 PM . Last Modified: β€Ž2024-03-22 04:25 AM

0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:03 PM . Last Modified: β€Ž2024-03-22 04:25 AM

Looks like someone didn't read my post πŸ˜›

Message was edited by: GamerBR

Message was edited by: GamerBR

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:03 PM . Last Modified: β€Ž2024-03-22 04:25 AM

0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:03 PM . Last Modified: β€Ž2024-03-22 04:25 AM

Unless you use a TRUE RMS multimeter, the measuraments made by the multimeter will be wrong.

The output wave of your UPS is a rectangular shaped type of wave aka stepped approximation to a sinewave. Cheap multimeters can't measure this kind of wave correctly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

Yeah, I confess I jumped into conclusions after reading the subject only. Sorry, I don' know what's going on with your UPS, it should be reading 115V +/- 10%.

Are you from Brazil? I am too. πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

Yes,I'm from Brazil too.
Just adding an info,the 93v test was while it had only a really small load into it(~15W),so I tried to plug more stuff on it to see if it would be the same voltage,at ~300W it is even worse,it went down by a little amount(92V).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

It's not normal these readings, but most power supplies can work at 90V or even less sometimes.

Have you tried measuring the output with another multimeter? Maybe your multimeter is not functioning correctly when measuring rectangular shapped waves for some reason.

A think one defective battery could also be the problem. Since your UPS runs off 24V battery bank, two 12V batteries in series to create one 24V bank, so perhaps one battery is failing, lowering the DC voltage output, but I think this is unlikely without some kind of warning from the UPS anyways. Maybe your unit has some kind of defect on the inverter output voltage regulation. I think the best thing you should do is to send your unit back to APC so they can check what's going on.

If the warranty has expired, these guys are authorized and trained by APC at the APC brazilian factory, to fix APC's upses:

http://www.csolutions.com.br/

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

The other multimeter I have isn't true RMS,so the reading`s cannot be trusted,anyway it's giving a bit lower voltage comparing to the other,like 3 or 4V less.
About the batteries,I tried running while on only of the banks of battery,same voltage on both,so the batteries are not the problem.
About the warranty,APC warranty in Brazil is 2 years right?My apc is a bit less than that,but I [almost for sure] voided my warranty by modding the battery connector to plug in a battery desulfator on it(the problem is not from it,I tried it with it disconnected and the voltage stills the same,and just after buying the UPS I did the same tests and the voltage were already lower than 100V,it's just that only now I started bothering about it).
I don't feel like paying to fix an UPS that's working for my needs and I'm a DIY person,I would prefer fixing it by myself πŸ˜›

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

Well, I think you might have voided the warranty by doing what you did, so you have two options. Check all the internal stages responsible for producing AC power locally or have someone do it for you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:04 PM . Last Modified: β€Ž2024-03-22 04:25 AM

How was this problem discovered? Did the UPS previously work properly? You say that all your equipment works properly. It is HIGHLY likely that your "true-RMS" multimeter is in fact, NOT True-RMS. This is very likely given that the reading between your two multimeters are very similar, which would make perfect sense given they are both NON-true RMS.

So are simple devices, such as an incandescent light bulb, not working properly while the UPS is operating on-battery? Of course, a light bulb will go very dim when the UPS goes on-battery if what you are saying is true about the voltage dropping to near 90vAC. No multimeter needed to perform this conclusive test.

I think this would perhaps be the best, if not most simple test you can try.

Does the UPS report through software that is is providing 90v, or does it indicate normal 115v battery output?

I believe there to be no problem, other than the way your multimeter was marketed as being true-RMS -- which is very likely is not.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of