Unexpected shutdown of SURT10000XLI

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Unexpected shutdown of SURT10000XLI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

0 Likes
5
1550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

Unexpected shutdown of SURT10000XLI

hello all, please see the attach file for the log and data event for your reference.
the other day the ups was down around 3:48am base on the data event and around 8:00am we just found out that the UPS was down and we power up the unit, unit is still working fine, Model: SURT10000XLI, so we call our vendor to check the ups and they found out nothing wrong with the unit, so my question in my mind why the ups was down if all the parameters is normal? base on the data and log event no power failure occur that time.
But i notice from the Data event the %Cap is something wrong, need you help to understand the data. Thanks in advance

Attachments
Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:06 AM

0 Likes
0
1550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:06 AM

hello all, please see the attach file for the log and data event for your reference.
the other day the ups was down around 3:48am base on the data event and around 8:00am we just found out that the UPS was down and we power up the unit, unit is still working fine, Model: SURT10000XLI, so we call our vendor to check the ups and they found out nothing wrong with the unit, so my question in my mind why the ups was down if all the parameters is normal? base on the data and log event no power failure occur that time.
But i notice from the Data event the %Cap is something wrong, need you help to understand the data. Thanks in advance

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

0 Likes
0
1550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:07 AM

but if there is a internal fault why is it the unit right now is working fine and the bypass LED doesnt light up.
I send already to the apc support but as of this moment i haven't receive a feedback so far. That why i try this forum if somebody can held me to understand base on the event i send. Also have you notice that from 07/24/2009 10:31:40 and 07/28/2009 03:47:06 in between there's no event was captured but if you can see from the data event you can see that all interval was captured.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:06 AM

0 Likes
0
1550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:06 AM

Hi Hanz,

The event log not showing anything during that time period should be good since it means there were no problems with the UPS or the power during this time period. From these logs there is no way to tell exactly what the fault was. If it does happen again be sure to check the display on the unit and see if the fault LED is lit and if so what other LEDs are lit/flashing.

Anyone else have any thoughts on this?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:06 AM

0 Likes
0
1550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:06 AM

i would suggest directly connecting to the UPS and retrieving the fault codes directly from it.

to do this:

1.) put the UPS into bypass mode if you can.
2.) remove the network management card
3.) obtain the APC smart signaling serial cable, part number 940-0024 or 940-1524 and connect it to the back of the UPS
4.) use the port settings of 2400, 8, none, 1 stop bit, no flow control and establish a connection with the UPS.
5.) do the following:
-Enter Shift-Y – This returns “SM”
-Enter 1, wait a second or two (do NOT hit enter after this), Enter 1 again – This returns “prog”
-Enter Ctrl-U – this returns the fault code

if you're able to get this, paste to us what the returned value is.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:06 AM

0 Likes
0
1549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:06 AM

Hi all

Sorry for the late reply, i was out station for few weeks, anyway i send over the data i collecte once i got, coz right now they a ssigned another person to handle for this,BTW thanks for the reply..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:06 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:05 PM . Last Modified: ‎2024-03-21 01:06 AM

hello all, please see the attach file for the log and data event for your reference.
the other day the ups was down around 3:48am base on the data event and around 8:00am we just found out that the UPS was down and we power up the unit, unit is still working fine, Model: SURT10000XLI, so we call our vendor to check the ups and they found out nothing wrong with the unit, so my question in my mind why the ups was down if all the parameters is normal? base on the data and log event no power failure occur that time.
But i notice from the Data event the %Cap is something wrong, need you help to understand the data. Thanks in advance

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore