New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
UTS6H UPS question- Can i use ecoflow Delta 2 as UPS?
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-0801:38 PM
UTS6H UPS question- Can i use ecoflow Delta 2 as UPS?
With the prices of these battery packs going down, is there any issue using an Eco flow Delta 2 or delta 2 max battery as the UPS for the UTS instead of a normal UPS? It would reside next to panel plugged in so its always charged and would run circuits if power goes out. @BillP
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-0905:32 AM. Last Modified: 2025-09-1008:09 AM
Really comes down to what the connected loads are and how sensitive they are to transfer time.
Most computers can sustain the upper limit of 10 ms before shutting down / rebooting.
The following APC Resource Link provides a high level overview of the transfer time in the Smart-UPS Series for Line Interactive vs Online (Double Conversion) UPS Topolgy:
Review what the Eco Flow is capable of in terms of transfer time during a lights out / grid down event.
If it exceeds 10 milliseconds than that is something to consider if sensitive electronics are present like a server.
You’ll want to pay special attention and validate how the UTS reacts with the Eco Flow when the two are mated together.
You don’t want to find out one or both devices exhibit any kind of relay flutter / bounce!
As such conditions are one of the main reasons for a failed ATS, UPS as the relays begin to rapidly toggle between open / close causing contact arcing and ultimately results in a relay weld condition! ☝️
Another option is to install a (manual) maintenance bypass switch if the condition I noted up above is seen.