UTS6H Neutral Leads on System Board Reversed on J32 and J33

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS6H Neutral Leads on System Board Reversed on J32 and J33
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
117
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
3
1189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

UTS6H Neutral Leads on System Board Reversed on J32 and J33

When we installed our hardware kit, and followed the instructions, the diagrams in the manual said to hook the neutral lead from the terminal block from the hardwire kit into the J33 lug off of the system board. The problem is that the original inlet that was removed from the unit (to make way for the hardware kit) had its neutral tied to J32, not J33. J33 was and still is occupied by the convenience outlet/IEC320 neutral lead. It came like that from the factory new. So, the decision had to be made: follow the instructions and use J33 for the hardware kit (and presumably change what came from the factory and move J33 to J32 for the convenience outlet neutral), or to assume there is no unique requirements that require that the hardware kit be tied into J33. So I made the choice to plug the hardwire kit neutral into the J32 connector (which the old L5-30 inlet used to be plugged into) and not follow the directions.

So are the directions incorrect or did my unit come in with a factory defect and have the inlet presided to J32 and not what appears to be the proper J33 according to the directions? Anyone else see this issue?

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • hardwire
  • j32
  • j33
  • kit
  • neutral
  • uts
  • uts6
  • uts6h
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
0
1189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

in regards to two neutrals, i know for the UTS10BI -due to the AWG used - a single #8 cannot fit so two #10 are used.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
0
1189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

I'm having the same problem with my new UTS6H. I'm not sure whether I should move the white wire from J33 to J32, and then connect the white wire. The hardware kit instructions also did not say to remove one of the white wires (which appears to be unused) at it did with the Brown wires.

Did you try move the current J33 to J32, and did you get rid of one of the white wires? Did it work?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
0
1189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

Just an update today. I spoke with APC tech support. They said that its the same neutral bus, so either J32 or J33 can be used to attach one of the neutral (white) wires, and the unused neutral (white) wire can remain unused (or removed).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
0
1190
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

in regards to two neutrals, i know for the UTS10BI -due to the AWG used - a single #8 cannot fit so two #10 are used.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore