MATRIX 5000 - NETWORK COMMUNICATION

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • MATRIX 5000 - NETWORK COMMUNICATION
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
3
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

MATRIX 5000 - NETWORK COMMUNICATION

We're in the UPS business and over time have accumulated several of these great old Matrix 5000 units. Our youngest unit is from 2004 and has a functional smart slot with a smart card connection within the slot. We want to use this UPS for a couple of months at a site until our customer relocates.
Does anyone know if that smart slot will take an AP9617 WEB card or must it be an AP9606 or perhaps even earlier? We no longer have any AP9606's in stock.
We also have an APC Powernet SNMP Adaptor (Serial Number A9403...) Module that plugs into the serial port on the back of the APC UPS that I presume should also work on this 2004 Matrix UPS. The Module is separately powered from a power supply that plugs into the UPS.
The interface cable to a computer from the Adaptor's Serial port must be female to female as the adaptors Serial port is male, as is the serial port on our old Dell laptop. We have a 940-0103A cable (female/female) used to interface to the relatively new APC Battery Monitoring unit. I'm hoping that cable will work.
Is there anyone around who knows about communications on the Matrix 5000 UPS system?

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • communication
  • matrix
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

Thanks VOIDSTAR for your help. We have some AP9617 cards in stock. We'll try it directly in the smart slot of the Matrix unit.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

The AP9617 supports the Matrix UPS so I would expect it to work in the SmartSlot.

I'm guessing your module that plugs into the UPS serial port is an APC SmartSlot Expansion Chassis (AP9600) with a AP9605 card installed. It can also accept an AP9617 and other SmartSlot cards. It is intended to be plugged directly into the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
0
1232
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

If you can't put it directly into your Matrix unit (I'm told really old units don't have the standard SmartSlot slot), then you can put it into the AP9600 expansion chassis and plug that into your Matrix.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
0
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

Thanks VOIDSTAR for your help. We have some AP9617 cards in stock. We'll try it directly in the smart slot of the Matrix unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore