Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

UTS6H - LCD Display

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS6H - LCD Display
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
2
1987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

UTS6H - LCD Display

I noticed today the LCD display on my UTS6H transfer switch was screwed up.  

If I reset the switch (turn off all power) and restart, its ok for a while but then it happens again.

Is this a bug or something? ideas?LCD

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
0
1986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

I think I can answer my own question. I ran a 30A generator feed (2 x 10AWG) via EMT using the top 1/2" hole, on the right side of the main board, passing by the logic board and to the terminal block (bottom right).

There had to be some sort of emissions back fed from those wires that caused interference as it passed by the logic board. This made sense as a restart of the APC cleared the issue, but only temporarily. Once moved the EMT (and conductors) to the bottom right 3/4" hole (and not passing by the logic board at all), the problem went away.

 

The APC had been mounted for over a year with no issues, and the generator fed the APC out of the back (into the garage where the generator usually was). We had concern over the carbon monoxide running the generator in the garage, and decided to run 40ft of 10/2 cable to our back stair where the generator can sit outside (and well vented).

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
0
1987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

I think I can answer my own question. I ran a 30A generator feed (2 x 10AWG) via EMT using the top 1/2" hole, on the right side of the main board, passing by the logic board and to the terminal block (bottom right).

There had to be some sort of emissions back fed from those wires that caused interference as it passed by the logic board. This made sense as a restart of the APC cleared the issue, but only temporarily. Once moved the EMT (and conductors) to the bottom right 3/4" hole (and not passing by the logic board at all), the problem went away.

 

The APC had been mounted for over a year with no issues, and the generator fed the APC out of the back (into the garage where the generator usually was). We had concern over the carbon monoxide running the generator in the garage, and decided to run 40ft of 10/2 cable to our back stair where the generator can sit outside (and well vented).

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

0 Likes
0
1986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:06 PM . Last Modified: ‎2024-03-21 03:56 AM

This transfer switch has worked great until just a few days ago... the display keeps screwing up like the picture in the first post. Functionally I think it is still fine, and just the display seems affected.  I'm baffled as to why it would act up all of a sudden.

Also, these seem to be very hard to find if one wanted to replace it too. Not many places stock them.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.