Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84522members
353759posts

UTS6H - LCD Display

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
2
202

UTS6H - LCD Display

This question was originally posted by Michelle on APC forums on 12/24/2016


I noticed today the LCD display on my UTS6H transfer switch was screwed up.  

If I reset the switch (turn off all power) and restart, its ok for a while but then it happens again.

Is this a bug or something? ideas?LCD


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
202

Re: UTS6H - LCD Display

This reply was originally posted by Michelle on APC forums on 12/31/2016


I think I can answer my own question. I ran a 30A generator feed (2 x 10AWG) via EMT using the top 1/2" hole, on the right side of the main board, passing by the logic board and to the terminal block (bottom right).

There had to be some sort of emissions back fed from those wires that caused interference as it passed by the logic board. This made sense as a restart of the APC cleared the issue, but only temporarily. Once moved the EMT (and conductors) to the bottom right 3/4" hole (and not passing by the logic board at all), the problem went away.

 

The APC had been mounted for over a year with no issues, and the generator fed the APC out of the back (into the garage where the generator usually was). We had concern over the carbon monoxide running the generator in the garage, and decided to run 40ft of 10/2 cable to our back stair where the generator can sit outside (and well vented).

See Answer In Context

Attachments
2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
203

Re: UTS6H - LCD Display

This reply was originally posted by Michelle on APC forums on 12/31/2016


I think I can answer my own question. I ran a 30A generator feed (2 x 10AWG) via EMT using the top 1/2" hole, on the right side of the main board, passing by the logic board and to the terminal block (bottom right).

There had to be some sort of emissions back fed from those wires that caused interference as it passed by the logic board. This made sense as a restart of the APC cleared the issue, but only temporarily. Once moved the EMT (and conductors) to the bottom right 3/4" hole (and not passing by the logic board at all), the problem went away.

 

The APC had been mounted for over a year with no issues, and the generator fed the APC out of the back (into the garage where the generator usually was). We had concern over the carbon monoxide running the generator in the garage, and decided to run 40ft of 10/2 cable to our back stair where the generator can sit outside (and well vented).

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
202

Re: UTS6H - LCD Display

This reply was originally posted by Michelle on APC forums on 3/2/2018


This transfer switch has worked great until just a few days ago... the display keeps screwing up like the picture in the first post. Functionally I think it is still fine, and just the display seems affected.  I'm baffled as to why it would act up all of a sudden.

Also, these seem to be very hard to find if one wanted to replace it too. Not many places stock them.