Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84855members
354324posts

UTS10BI fuse behavior

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
moran_apc
Ensign
Ensign
0 Likes
2
475

UTS10BI fuse behavior

This was originally posted on APC forums on 12/6/2019


What I'm reporting may be already known to the more knowledgeable members of this forum but it was news to me. I experienced a simple short in a bedroom wall circuit that seemed to trip a circuit breaker in the regular panel. However no breaker was tripped yet the outlets in that room were all dead. I didn't even think to look at the UTS 10BI as I thought it's protective behavior was only when my generator was the power source. However, as I learned from a licensed electrician, the fuses on that circuit in the UTS  open faster than the breakers can and it was the replacement of that fuse that returned service to that room. So as a rule, at least for me, when I experience a current loss due to a short I'll check the UTS first.


Accepted Solutions
moran_apc
Ensign
Ensign
0 Likes
0
474

Re: UTS10BI fuse behavior

Thank you for the additional useful information.

See Answer In Context

Tags (1)
2 Replies 2
dferrero_apc
Ensign
Ensign
0 Likes
1
475

Re: UTS10BI fuse behavior

This was originally posted on APC forums on 5/2/2020


Yes, the glass fuse will likely blow before a slower circuit breaker trips. To test your glass fuse, put your multi-meter into continuity mode or resistance and measure. It should have near zero resistance if the fuse is still good. If it is blown, the resistance is basically infinite.

Two other things to check in the UTS config. Ensure the UTS fuse is equal to the breaker (15A = 15A). Ensure the UTS is configured for the fuse used. In other words, if you use a 20A glass fuse in the UTS, ensure that circuit is configured for that 20A fuse.

 

moran_apc
Ensign
Ensign
0 Likes
0
475

Re: UTS10BI fuse behavior

Thank you for the additional useful information.