Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

UTS10BI circuit status when connected to UPS?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS10BI circuit status when connected to UPS?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2127
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
paulsnyder_apc
Crewman paulsnyder_apc
Crewman

Posted: ‎2021-06-29 11:08 PM

0 Likes
2
237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM

UTS10BI circuit status when connected to UPS?

This was originally posted on APC forums on 3/25/2013


I recently connected an APC Smart UPS (SMT1500) to my UTS10BI.  The UPS is plugged into the convenience outlet on the front panel of the UTS10BI and I have the UTS10BI supplied power cord connected to the front panel inlet to the back outlets on the UPS.  I then configured on the UTS10BI the circuit (Circuit #4) that has my computer and two wireless routers (includes Internet modem) on it.  I used the pre-configured default settings for "Computer" on that circuit.  So, to confirm the settings, the circuit is uninterruptable.  Then I flipped off the breaker to that circuit in my main panel to simulate the power going out.  The results are as follows:

1. The UPS picked up and fed power to the computer circuit. Good!

2. The convenience outlet (Circuit #1) on the UTS10BI went into fault mode with no power feeding the UPS.  I did not flip off the main breaker or the circuit breaker in the main panel feeding Circuit #1, just the circuit breaker feeding the computer circuit on the UTS10BI.  I do not understand why it did this. Can you help explain why?  Is there something about the UTS10BI circuit settings for Circuit #1 that I should be aware of?

3. I flipped the breaker in the main panel feeding the computer circuit in the UTS10BI back on.  I then checked the status of the circuit (#4) on the UTS10BI and it shows the power source as the UPS.  I expected it to show Utility.  After I thought about it, maybe it is suppose to read UPS. Am I right?  The UPS is showing in its' display the amount of the load, but it does not indicate it is drawing from its' battery and Circuit #4 is receiving power.

Any input/help would be appreciated.  I am just trying to figure out the nuances of my setup.

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
paulsnyder_apc
Crewman paulsnyder_apc
Crewman

Posted: ‎2021-06-29 11:08 PM

0 Likes
0
237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM

This was originally posted on APC forums on 3/26/2013


Thank you for the input.  I tried recreating the circuit fault and can't.  So at this point it becomes a moot issue.

With regards to Circuit #4 showing the power source as "UPS" when set up as "Uninterruptible", apparently this is the way it should be.  The following is from the owner's manual.

UNINTERRUPTIBLE

-there is continuous backup power supplied by a UPS. Utility power flows into the UPS and from

the UPS to the connected load. This provides power and protection for the load during any utility power fluctuation.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:08 PM

0 Likes
0
237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM

This reply was originally posted by Secret on APC forums on 3/25/2013


Circuit 1 is what feeds power to the Convenience Outlet on the UTS. When cutting power to circuit 4, circuit 1 must now support it's own load as well as circuit 4's load. If circuit 1 senses too much current draw now that it has the extra load, it will enter an overload condition and stop passing power. This may explain why the UPS is now on battery. It may be best to reduce the combined load between Circuit 1 and Circuit 4, to something below the 15amp maximum.

Reply

Link copied. Please paste this link to share this article on your social media post.

paulsnyder_apc
Crewman paulsnyder_apc
Crewman

Posted: ‎2021-06-29 11:08 PM

0 Likes
0
238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM

This was originally posted on APC forums on 3/26/2013


Thank you for the input.  I tried recreating the circuit fault and can't.  So at this point it becomes a moot issue.

With regards to Circuit #4 showing the power source as "UPS" when set up as "Uninterruptible", apparently this is the way it should be.  The following is from the owner's manual.

UNINTERRUPTIBLE

-there is continuous backup power supplied by a UPS. Utility power flows into the UPS and from

the UPS to the connected load. This provides power and protection for the load during any utility power fluctuation.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc