Just bought a brand new BX1500G, it says replace the battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Just bought a brand new BX1500G, it says replace the battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

0 Likes
9
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

Just bought a brand new BX1500G, it says replace the battery

The battery appears to be fully charged and the UPS works fine when I unplug the power, it says it will keep my equipment running for 45 minutes.  However, the battery indicator is flashing and the unit is beeping continuously, indicating that the battery should be replaced.  Is this normal for a brand new UPS with a fully charged battery?  I didn't find anything concerning this in the manual.

Phil

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:09 PM . Last Modified: ‎2024-03-20 12:52 AM

0 Likes
0
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:09 PM . Last Modified: ‎2024-03-20 12:52 AM

The one thing you could try is a UPS braindead. For this model, you'll need to turn off your attached equipment to the UPS and unplug it. Then, turn the UPS off as well and unplug it from the wall. Disconnect the UPS battery completely and then hold down the power button afterwards on the UPS for about 10-20 seconds to ensure all capacitors are discharged. Reconnect the battery and turn the UPS back on and see what you get. You can also connect your computer and other items back up too if you'd like. Remember to wait for the UPS self test to complete when the UPS powers up.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

0 Likes
0
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

Hello - the unit should be left to charge for at least 24 hours after unpacking it and installing it. So, just give it 24 hours without touching it or running any tests to see if that issue clears up.

When the units are in storage for a while (like on the shelf at a retailer), the battery voltage can be below a certain threshold so the UPS can't see it. After it charges up, it should go away. Let us know if it does not.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

0 Likes
0
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

It has been about 27 hours now and the battery indicator is still blinking.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

0 Likes
0
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

Can you give me the first few digits of the serial number off the UPS so we can see how old it is? The other thing I would try is with a non-critical load on the UPS, can you plug something into the battery back up outlets and then pull the plug on the UPS to see if it actually switches to battery power even though it indicates the battery is disconnected? If it works, then it tells me it could be a potential UPS issue. If it does not work, perhaps the battery was stored too long and cannot properly charge up. The serial number is on the white sticker on the back of the UPS - something like JB1224 is all I need. If that is the case, tech support should be able to send you a new battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

0 Likes
0
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

I could not find a white sticker on the back of the UPS.  I found one on the bottom that had the model number and another number that was 4B124OPO2447.  I just looked at the box and it has that as the serial number also.  I unplugged the UPS from the power outlet, it said it was delivering 72 watts of power which it said was an 8% load and it was going to keep my equipment running for 69 minutes.  I only waited about 90 seconds and then I re-connected it to the power outlet.  There is an inspection sticker on the side of the unit, it passed the inspections on 10-1-2012.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

0 Likes
0
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

Ok, yes that is the serial number. Thank you. So in all your testing, your equipment connected to the UPS never turned off - either in your first test or second?

Is the battery indicator still flashing as of now? It seems like this is a false alarm but obviously the UPS should not have that indicator flashing even though the battery is truly connected per your testing results and the fact it keeps your equipment up and running.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

0 Likes
0
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:08 PM . Last Modified: ‎2024-03-20 12:52 AM

Yes, in all my testing, the equipment connected to the UPS never turned off, yet that battery indicator is still blinking.  Is there some way to reset it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:09 PM . Last Modified: ‎2024-03-20 12:52 AM

0 Likes
0
2404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:09 PM . Last Modified: ‎2024-03-20 12:52 AM

The one thing you could try is a UPS braindead. For this model, you'll need to turn off your attached equipment to the UPS and unplug it. Then, turn the UPS off as well and unplug it from the wall. Disconnect the UPS battery completely and then hold down the power button afterwards on the UPS for about 10-20 seconds to ensure all capacitors are discharged. Reconnect the battery and turn the UPS back on and see what you get. You can also connect your computer and other items back up too if you'd like. Remember to wait for the UPS self test to complete when the UPS powers up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:09 PM . Last Modified: ‎2024-03-20 12:51 AM

0 Likes
0
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:09 PM . Last Modified: ‎2024-03-20 12:51 AM

Angela -

Thank you for all your help, that fixed it!

Phil

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:09 PM . Last Modified: ‎2024-03-20 12:51 AM

0 Likes
0
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:09 PM . Last Modified: ‎2024-03-20 12:51 AM

You're very welcome! wink

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore