Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84606members
353881posts

UTS10BI Powering input 2 with a small generator

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
EDMC_apc
Crewman
Crewman
0 Likes
2
111

UTS10BI Powering input 2 with a small generator

This was originally posted on APC forums on 5/23/2010


Hi

I would like to power my UTS10BI (Input2) with a Honda EU2000i generator. The generator has a Max output of 2000 Watts, 17 Amps at 120 volts. If I set the Input 2 power rating at (0-1800Watts) will this generator be OK?
I have a 4000 Watt generator powering Input 1.
Thank You
Eddie


Accepted Solutions
EDMC_apc
Crewman
Crewman
0 Likes
0
111

UTS10BI Powering input 2 with a small generator

This was originally posted on APC forums on 5/23/2010


Hi

I would like to power my UTS10BI (Input2) with a Honda EU2000i generator. The generator has a Max output of 2000 Watts, 17 Amps at 120 volts. If I set the Input 2 power rating at (0-1800Watts) will this generator be OK?
I have a 4000 Watt generator powering Input 1.
Thank You
Eddie

See Answer In Context

2 Replies 2
EDMC_apc
Crewman
Crewman
0 Likes
0
111

Re: UTS10BI Powering input 2 with a small generator

This was originally posted on APC forums on 5/26/2010


The input2 max power rating is 1800 watts. As you said, this may be a good thing. 1800 watts with this little generator will be just enough power to keep the heat on and the refrigerator running during an extended New Hampshire power outage. Thank you for your help. Eddie