Hi
I would like to power my UTS10BI (Input2) with a Honda EU2000i generator. The generator has a Max output of 2000 Watts, 17 Amps at 120 volts. If I set the Input 2 power rating at (0-1800Watts) will this generator be OK?
I have a 4000 Watt generator powering Input 1.
Thank You
Eddie
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:05 PM . Last Modified: 2024-03-20 05:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:05 PM . Last Modified: 2024-03-20 05:49 AM
Hi
I would like to power my UTS10BI (Input2) with a Honda EU2000i generator. The generator has a Max output of 2000 Watts, 17 Amps at 120 volts. If I set the Input 2 power rating at (0-1800Watts) will this generator be OK?
I have a 4000 Watt generator powering Input 1.
Thank You
Eddie
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:05 PM . Last Modified: 2024-03-20 05:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:05 PM . Last Modified: 2024-03-20 05:49 AM
The input2 max power rating is 1800 watts. As you said, this may be a good thing. 1800 watts with this little generator will be just enough power to keep the heat on and the refrigerator running during an extended New Hampshire power outage. Thank you for your help. Eddie
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:05 PM . Last Modified: 2024-03-20 05:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:05 PM . Last Modified: 2024-03-20 05:49 AM
Hi
I would like to power my UTS10BI (Input2) with a Honda EU2000i generator. The generator has a Max output of 2000 Watts, 17 Amps at 120 volts. If I set the Input 2 power rating at (0-1800Watts) will this generator be OK?
I have a 4000 Watt generator powering Input 1.
Thank You
Eddie